[Bldg-sim] DX Cooling EIR Ratio Curve
eric wang
shaojieworld2006 at yahoo.com
Thu Feb 19 08:39:37 PST 2009
Jeff,
The system type is DX packaged single zone. From the hourly report, I found sometimes Temp correction to COOLING-EIR, Part load correction to COOLING-EIR and Operating EIR are zero when Cool on/off flag is on. Is there a specific condition that these parameters can equal zero?
Thanks a lot
Shaojie
--- On Tue, 2/17/09, Jeff Hirsch <Jeff.Hirsch at DOE2.com> wrote:
From: Jeff Hirsch <Jeff.Hirsch at DOE2.com>
Subject: Re: [Bldg-sim] DX Cooling EIR Ratio Curve
To: shaojieworld2006 at yahoo.com
Cc: glenn.haynes at rlw.com
Date: Tuesday, February 17, 2009, 1:26 PM
don't forget that the COOL-FT-MIN is used as a minimum
value for the curve input for the extering condenser temperture.
COOL-FT-MIN is also for the evap min temperature into
the curve. So low OA temps and low entering wetbulb will not be
fully reflected into the curve values.
COOL-FT-MIN default
(cond temp curve low limit)
water cooled 60
evap cooled 50
air or evap pre-cooled 70
(evap temp curve low limit)
evap cooled COOL-MIN-T
all others COOL-MIN-T - 10.0
---
Jeff Hirsch
James J. Hirsch & Associates
12185 Presilla Road
Camarillo, CA 93012-9243 USA
phone: (805) 553-9000
fax: (805) 532-2401
email: Jeff.Hirsch at DOE2.com
web: http://DOE2.com
skype: jeffhirschcamarillo
----- Original Message -----
From: eric wang
To: Glenn Haynes
Cc: bldg-sim at lists.onebuilding.org bldg-sim at lists.onebuilding.org
Sent: Tuesday, February 17, 2009 9:22 AM
Subject: Re: [Bldg-sim] DX Cooling EIR Ratio Curve
Jonathan and Glenn,
Thanks a lot for your replies. However, the values I calculated by using return or mixing air wet bulb temperatures are still different to the number listed in the hourly report.
Thanks
Shaojie
--- On Fri, 2/13/09, Glenn Haynes <glenn.haynes at rlw.com> wrote:
From: Glenn Haynes <glenn.haynes at rlw.com>
Subject: RE: [Bldg-sim] DX Cooling EIR Ratio Curve
To: shaojieworld2006 at yahoo.com
Date: Friday, February 13, 2009, 3:08 PM
#yiv204744541 UNKNOWN {
FONT-FAMILY:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;}
#yiv204744541 #yiv1091583735 #yiv1091583735 P.MsoNormal {
FONT-SIZE:12pt;MARGIN:0in 0in 0pt;FONT-FAMILY:"Times New Roman";}
#yiv204744541 #yiv1091583735 LI.MsoNormal {
FONT-SIZE:12pt;MARGIN:0in 0in 0pt;FONT-FAMILY:"Times New Roman";}
#yiv204744541 #yiv1091583735 DIV.MsoNormal {
FONT-SIZE:12pt;MARGIN:0in 0in 0pt;FONT-FAMILY:"Times New Roman";}
#yiv204744541 #yiv1091583735 A:link {
COLOR:blue;TEXT-DECORATION:underline;}
#yiv204744541 #yiv1091583735 SPAN.MsoHyperlink {
COLOR:blue;TEXT-DECORATION:underline;}
#yiv204744541 #yiv1091583735 A:visited {
COLOR:purple;TEXT-DECORATION:underline;}
#yiv204744541 #yiv1091583735 SPAN.MsoHyperlinkFollowed {
COLOR:purple;TEXT-DECORATION:underline;}
#yiv204744541 #yiv1091583735 SPAN.EmailStyle17 {
COLOR:navy;FONT-FAMILY:Arial;}
#yiv204744541 UNKNOWN {
MARGIN:1in 1.25in;}
#yiv204744541 #yiv1091583735 DIV.Section1 {
}
The wet bulb temperature refers to that entering the evaporator, which is the return air wet bulb temperature.
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of eric wang
Sent: Friday, February 13, 2009 1:48 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] DX Cooling EIR Ratio Curve
Hi,
I used the default DX Cooling EIR Ratio Curve (DX-Cool-Cap-fEWB&OAT) in eQUEST. The variables are t entering wetbulb and t enter condenser. I assume these refer to outside air wet and dry bulb temperatures. After exporting outside air wet and dry bulb temperatures in hourly report, the value of "Temp correction to COOLING-EIR" I calculated is different to the one in the hourly report by using the curve coefficients. Can anyone point out if my understanding is correct?
Thanks a lot for your help
Shaojie
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090219/1f2340c6/attachment-0001.htm>
More information about the Bldg-sim
mailing list