[Bldg-sim] Converting TMY, BIN and CSV files

Mathew Higgins higgins at edi-arch.com
Mon Feb 2 15:58:45 PST 2009


I've read through previous posts and attempted several iterations of 
converting to BIN with no avail. I can get the NEWTH.TMP file to appear, 
but with no information. Below is my step-by-step process, with info 
from previous posts. (Also, where is the "EXENT directory ?" I've been 
saving to the directory where the processor/excutables live.)

Get "real time" CSV weather data from Energy Plus website: 
http://apps1.eere.energy.gov/buildings/energyplus/cfm/weatherdata/weather_request.cfm

Remove commas (or file breaks) from CSV file(s) in order obtain a TMY file

Using the DOE2 Conversion tool (http://doe2.com/index_Wth.html) use the 
following steps:

  <>
*1.    *Copy your TMY2 file to DOE2's EXENT directory and rename to 
WEATHR.TMP (*NOT* "WEATHR.TMP.TXT")

*2.    *Create a file called INPUT.TMP in the EXENT directory (*NOT* 
"INPUT.TMP.TXT"), /removing *IWEC *from in front of the station name*
*/

*3.    *In the INPUT.TMP file, put the following text. Be sure to 
replace the city, state, and station number as appropriate for your 
location. You can find this information in the first line of the TMY2 file.

  <>
PACK
ALBUQUERQUE INTERNATIONAL TMY2
TMY2  72365
STAT
END  <>

*4.* Run the DOEWTH.EXE executable (it will automatically use the 
WEATHR.TMP and INPUT.TMP files above as inputs). This will create a 
NEWTH.TMP file in the EXENT directory that is your bin weather file for 
use with DOE2. Just rename to Location.bin and you're set.


My WEATHR.TMP file looks like this, after removing the last digit of the 
weather station ID:

72365 ALBUQUERQUE INTERNATIONAL     4 - 07 00 N 35 02 W 106 36 + 1631
 2008 12917999999999999?09999?09999?09999?09999?09999?09999?099?099?0  
20A7-140A7999?01014A7 10A7 51A7 161A7 
7620A71000A79999999999999?0999?0999?099?0
 2008 12918999999999999?09999?09999?09999?09999?09999?09999?099?099?0  
10A7-140A7999?01014A7 20A7 46A7 161A7 
7620A71000A79999999999999?0999?0999?099?0
 2008 12919999999999999?09999?09999?09999?09999?09999?09999?099?099?0   
0A7-150A7999?01013A7360A7 36A7 161A7 
7620A71000A79999999999999?0999?0999?099?0
 2008 12920999999999999?09999?09999?09999?09999?09999?09999?099?099?0 
-10A7-160A7999?01013A7350A7 36A7 161A7 
7620A71000A79999999999999?0999?0999?099?0
 2008 12921999999999999?09999?09999?09999?09999?09999?09999?099?099?0 
-10A7-150A7999?01013A7  0A7  0A7 
161A777777A70000A79999999999999?0999?0999?099?0
 2008 12922999999999999?09999?09999?09999?09999?09999?09999?099?099?0 
-30A7-120A7999?01012A7310A7 15A7 
161A777777A70000A79999999999999?0999?0999?099?0
 2008 12923999999999999?09999?09999?09999?09999?09999?09999?099?099?0 
-50A7-110A7999?01012A7  0A7  0A7 
161A777777A70000A79999999999999?0999?0999?099?0
 2008 12924999999999999?09999?09999?09999?09999?09999?09999?099?099?0 
-40A7-110A7999?01011A7  0A7  0A7 
161A777777A70000A79999999999999?0999?0999?099?0
 2008 130 1999999999999?09999?09999?09999?09999?09999?09999?099?099?0 
-40A7-120A7999?01009A7140A7 26A7 
161A777777A70000A79999999999999?0999?0999?099?0
 2008 130 2999999999999?09999?09999?09999?09999?09999?09999?099?099?0 
-40A7-110A7999?01009A7190A7 31A7 
161A777777A70000A79999999999999?0999?0999?099?0
 

Much thanks for additional consideration to this belabored issue.

Matthew Higgins, LEED AP + ASHRAE-HBDP
Technical Specialist
Environmental Dynamics, Inc.
Architecture and Sustainability Consulting Services
505.242.2851

Any data provided by the Consultant, verbal or written, are to be considered opinions of building energy and/or daylight performance. The Client understands that the Consultant has no control of occupant habits, equipment or material performance or characteristics, site or climate conditions or the Contractor's method of assembly, and that the Consultant's opinions regarding building energy/daylight performance are made on the basis of the Consultant's professional judgment and experience. The Consultant makes no warranty, express or implied, that the energy/daylight performance of the building will not vary from the Consultant's opinion of building energy/daylight performance.



Karen Walkerman wrote:

> Bill,
>
> my file looks like this:
>
> 14742 BURLINGTON             VT  -5 N 44 28 W  73  9   104
>  86010101000000000000?00000?00000?00000?00000?00000?00000?010A710A70011A7-028A7076A70994A7190A7036A70080A701006A70999099999009E7036F8015A700E7
>  86010102000000000000?00000?00000?00000?00000?00000?00000?010A710A70006A7-022A7082A70995A7210A7015A70080A700823A70999099999009E7036F8015A700E7
>  86010103000000000000?00000?00000?00000?00000?00000?00000?010A710A70017A7-067A7054A70995A7260A7062A70113A701829A70999999999007E7036F8015A700E7
>  86010104000000000000?00000?00000?00000?00000?00000?00000?010A710A70011A7-067A7057A70996A7260A7077A70113A701829A70999999999007E7036F8015A700E7
>  86010105000000000000?00000?00000?00000?00000?00000?00000?010A710A7-017A7-056A7075A70996A7320A7077A70113A700975A70999099999008E7036F8015A700E7
>  86010106000000000000?00000?00000?00000?00000?00000?00000?010A710A7-028A7-067A7075A70998A7340A7052A70097A701219A70999099999007E7036F8015A700E7
>  86010107000000000000?00000?00000?00000?00000?00000?00000?010A710A7-033A7-044A7092A70999A7320A7057A70012A700213A70999099099008E7036F8015A700E7
>
> ... etc.  The file I'm trying to convert is simply the downloaded 
> version from the nrel website.  I can get my weather data into this 
> sort of text format, so I just need to be able to get it back to bin!!!
>
> However, I keep getting the following error:
>
> --- ERROR --- END OF FILE READ.  TAPE TYPE TMY2 
>
> Some solutions others have suggested that have not worked so far...
>
> 1.  Try using energy plus to convert the file to an energy plus 
> format, just to make sure that the source file is valid--Energy Plus 
> had no problem with the file
>
> 2.  Is the INPUT.TM2 text in exactly the right format (correct number 
> of spaces and station ID numbers)--Yes, this is exactly as 
> demonstrated here 
> (http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/2008-May/007524.html), 
> with two spaces between the "TMY2" and station ID on line 3, and a 
> 5-digit station ID which matches the WEATHER.TMP file.
>
> 3.  When the files are saved as TMP files, are they WEATHER.TMP.TXT 
> and INPUT.TMP.TXT, or are they truly TMP files--They are truly TMP 
> files.  In the explorer, under "TYPE" they are identified as TMP files.
>
> Thanks everyone for your suggestions please let me know if you have 
> any others.
>
> --
> Karen
>
>
>
> On Tue, Dec 9, 2008 at 11:59 AM, Bill Talbert <btalbert at aeieng.com 
> <mailto:btalbert at aeieng.com>> wrote:
>
>     Karen,
>     Is your data in TMY format or is it a standard text file? Attached
>     is a sample text file that I created for custom weather data that
>     can then be packed into a .bin format with the PKAFT.bat in the
>     DOE weather utilities. The TMY format file looks a little
>     different. Below are a few lines from a tmy file:
>      
>      93721 BALTIMORE              MD  -5 N 39 11 W  76 40    47
>      65010101000000000000?00000?00000?00000?000000000000000000A700A70000A7067A7061A71026A7290A7041A70322A777777A70999999999007E7061F8000A710E7
>      65010102000000000000?00000?00000?00000?000000000000000000A700A70000A7067A7061A71026A7290A7041A70322A777777A70999999999007E7061F8000A710E7
>      65010103000000000000?00000?00000?00000?00000?0000000000000A700A7011A7061A7069A71027A7280A7021A70322A777777A70999999999008E7061F8000A710E7
>     If your TMY file does not look similar, I don't think the tm2 to
>     bin tool will work.
>      
>     If your data is not in valid tmy format, you can arrange it using
>     a spreadsheet tool with 'concatenate' function so that everything
>     is in one column with appropriate spacing and then save it as a
>     text file. Rename the file with a .ft extension and edit the
>     PKAFT.bat to referenced the appropriate file.
>     Regards,
>     Bill
>      
>      
>     Bill Talbert, PE, LEED® AP
>     Mechanical Systems
>     Phone: (608) 441-6677
>     E-mail: btalbert at aeieng.com <mailto:btalbert at aeieng.com>
>
>     Affiliated Engineers Inc.
>     5802 Research Park Blvd.
>     Madison, WI. 53719
>     Tel. (608) 238-2616
>     Fax. (608) 238-2614
>
>     >>> "Karen Walkerman" <kwalkerman at gmail.com
>     <mailto:kwalkerman at gmail.com>> 12/9/2008 10:29 AM >>>
>
>     Hi Scott,
>
>     Thanks for your response.  I tried your method (on both Vista and
>     XP machines), and the files are created, but the NEWTH.TMP file
>     has no info in it (0KB) any thoughts?
>
>     Thanks again,
>
>     --
>     Karen
>
>     On Tue, Dec 9, 2008 at 11:16 AM, Horowitz, Scott
>     <Scott_Horowitz at nrel.gov <mailto:Scott_Horowitz at nrel.gov>> wrote:
>
>         Karen,
>
>          
>
>         See if my past instructions on the matter help:
>
>         http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/2008-May/007524.html
>
>          
>
>         Scott
>
>          
>
>         --
>
>         Scott Horowitz
>
>         Center for Buildings & Thermal Systems
>
>         National Renewable Energy Laboratory
>
>         1617 Cole Blvd.
>
>         Golden, CO 80401
>
>         303.384.7560
>
>          
>
>         ------------------------------------------------------------------------
>
>         *From:* bldg-sim-bounces at lists.onebuilding.org
>         <mailto:bldg-sim-bounces at lists.onebuilding.org>
>         [mailto:bldg-sim-bounces at lists.onebuilding.org
>         <mailto:bldg-sim-bounces at lists.onebuilding.org>] *On Behalf Of
>         *Karen Walkerman
>         *Sent:* Tuesday, December 09, 2008 9:09 AM
>         *To:* bldg-sim at lists.onebuilding.org
>         <mailto:bldg-sim at lists.onebuilding.org>
>         *Subject:* [Bldg-sim] Converting TMY, BIN and CSV files
>
>          
>
>         Hi All,
>
>         I've seen a bunch of questions on the list-serve about
>         creating custom weather files, but never figured out how to do
>         it myself.
>
>         I've been able to create a custom CSV file (and then removed
>         all commas), so I should now have a custom TMY file.  How do I
>         get it into BIN format so eQuest can read it?  I downloaded
>         the conversion files from DOE2
>         (http://doe2.com/index_Wth.html), but can't get them to work
>         so far.  Does anyone have a more complete description of how
>         to make them work?  Also, I am running Vista... not sure if
>         this is a problem as the conversion programs are DOS based.
>
>         Thanks,
>
>         --
>         Karen
>
>
>         _______________________________________________
>         Bldg-sim mailing list
>         http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>         To unsubscribe from this mailing list send  a blank message to
>         BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>         <mailto:BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>------------------------------------------------------------------------
>
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>  
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090202/9bfe78fc/attachment-0001.htm>


More information about the Bldg-sim mailing list