Is the 0.2 to 0.5 ACH based on blower door testing?  Did you apply some
sort of conversion to get from the blower door pressure differential to
a typical real world pressure?

 

Doug Maddox

The Weidt Group

________________________________

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James V.
Dirkes II P.E.
Sent: Monday, February 09, 2009 7:30 AM
To: 'Eric Studer'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Infiltration Schedule

 

Dear Andy and Eric,

 

My past experience with industrial buildings (manufacturing, assembly,
warehouses, etc) indicates that a good building has an AVERAGE winter
AC/hr of ~0.2.  Poor buildings are on the order of 0.5 (or more!) 

 

This doesn't address residences (which often have much higher
infiltration rates) offices or high rises, but it may be helpful.  Most
of the literature I'm familiar with indicates that infiltration is
normally a lot higher than is generally assumed.  My experience confirms
that.

 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

 

	 

	
________________________________


	From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Eric Studer
	Sent: Monday, February 09, 2009 6:42 AM
	To: bldg-sim at lists.onebuilding.org
	Subject: Re: [Bldg-sim] Infiltration Schedule

	I tend to model an air exchange rate of 0.15 ACH in perimeter
spaces during unoccupied hours (e.g. outside air fans are off with
dampers closed) for new buildings (even if they have air barriers).
Vestibules, conditioned loading docks, etc usually get higher air change
rates.  Zones with no exterior exposure should not be modeled as having
any infiltration since there is not a way for air at outside conditions
to make it to these zones.  I assume no infiltration into plenum zones.


	 

	I am curious to know whether or not this seems reasonable based
on real world experience.  Andy, any thoughts?

	 

	Thanks,

	 

	Eric

	 

	Ph:   (781) 431-1100 ext 12
	Fax:  (781) 431-1109

	 

	
________________________________


	From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Andy hoover
	Sent: Friday, February 06, 2009 5:07 PM
	To: 'Talbert, Joshua'; bldg-sim at lists.onebuilding.org
	Subject: Re: [Bldg-sim] Infiltration Schedule

	 

	Hi all:

	 

	We do building envelope consulting and are very curious as to
what folks do and what rates they use whatever approach.  When looking
at buildings we find that most  infiltrate much more in the real world
than designers estimate and that the fluctuations are far greater than
predicted.  We would also love it if anyone has any experiences which
can be shared.

	 

	Thanks,

	 

	Andy 

	 

	Andy Hoover

	Principal

	The BEST Consultant, Inc.

	Office: 678-200-7648

	Fax:678-827-0574

	Cell: 678-793-1159

	 

	www.thebestconsultant.com

	 

	 

	
________________________________


	This message may contain confidential and/or privileged
information. If you are not the addressee or authorized to receive this
information for the addressee, you must not use, copy, disclose, or take
any action based on this message or information herein. If you have
received this message in error, please advise the sender immediately by
reply e-mail and delete this message. Thank you for your cooperation.

	
________________________________


	From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Talbert,
Joshua
	Sent: Friday, February 06, 2009 10:30 AM
	To: bldg-sim at lists.onebuilding.org
	Subject: [Bldg-sim] Infiltration Schedule

	 

	Howdy Bldg Sim peers!

	 

	While working on LEED Equest simulations I find that in an
effort to simplify I end up deleting the P-Inf and C-Inf Infiltration
Schedules all of the time and end just use "undefined" to simulate a
constant infiltration rate.  I was curious to know if anyone uses the
actual Infiltrations schedules, to emulate winds and or building
pressurization, and if so do you typically achieve more energy savings,
and do you find it worth the extra effort?

	 

	Thanks all and be well.

	 

	Josh

	Joshua W. Talbert P.E., LEED-AP

	Mechanical Engineer

	Hallam///ICS

	38 Eastwood Dr. Suite 200

	S. Burlington, VT 05403

	P: (802) 658-4891

	F: (802) 658-1457

	 

	 

	 

	
________________________________


	
	CONFIDENTIALITY NOTICE:
	The information contained in this transmission, as well as any
accompanying documents, constitutes confidential and/or legally
privileged information which is the property of Hallam-ICS. The
information is intended solely for the individual entity named on this
transmittal sheet. If you are not the designated recipient, you are
hereby notified that any disclosure, copying, distribution or taking any
action in reliance on this information is strictly prohibited. If you
received this in error, please contact the sender and delete the
material from any computer. Opinions, conclusions and the information in
this message that do not relate to the official business of my firm
shall be understood as neither given nor endorsed by it.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090209/9dbfd92a/attachment.htm>


More information about the Bldg-sim mailing list