[Bldg-sim] ASHRAE 90.1-2004 Packaged Terminal Heat Pump Efficiencies

Dan Jestico djestico at hilsonmoran.com
Tue Dec 1 08:34:19 PST 2009


Afternoon all,
 
We're trying to obtain the minimum CoP for a Packaged Terminal Heat Pump
in cooling mode for a new construction using table 6.8.1D in ASHRAE
90.1-2004 (SI edition) and the formula is proving to be somewhat
confusing. In the SI edition it is described as 
 
[3.60 - (0.213 x Cap/1000)]
 
Is this the same equation as listed in the imperial edition of
90.1-2004? If the max. unit capacity of 4.4kW is converted to Btu/hr
(approx 15024 Btu/hr, as per note c) and input to the formula, the
minimum CoP is only 0.4, which seems very low. However, if I use the
value in Watts in the equation, the minimum CoP comes out as a much more
reasonable 2.66. 
 
I can't seem to find any addenda on ASHRAE's website or additional
guidance on this matter and would very much appreciate any guidance you
can provide.
 
Many thanks for your help.

Dan.
 
DAN JESTICO 
 
HILSON MORAN
 
Members of the Italian, Emirates, U.K. and U.S. Green Building Councils
 
Direct Dial: 	
+44 (0)20 7940 8884
Mobile:
London:
+44 (0)7595 106 614
+44 (0)20 7940 8888
www.hilsonmoran.com <http://www.hilsonmoran.com/> 	
 
Please consider the environment before printing this email.
 
Registered No: 1233447 England. Registered Office: One Discovery Place,
Columbus Drive, Southwood West, Farnborough, Hampshire GU14 0NZ
 
This message is for the named person(s) use only and may contain
confidential, proprietary or legally privileged information. No
confidentiality or privilege is waived or lost by erroneous
transmission. If you receive this message in error, please immediately
delete it and all copies of it from your system, destroy any hard copies
of it and notify the sender. You must not, directly or indirectly, use,
disclose, distribute, print, or copy any part of this message if you are
not the intended recipient. Hilson Moran Partnership Ltd reserves the
right to monitor all email communications through its networks. Any
views expressed in this message are those of the sender, except where
the message specifically states them to be the views of Hilson Moran
Partnership Ltd. All transmissions are checked for viruses but all
recipients are advised to undertake their own virus checks as Hilson
Moran Partnership Ltd will not take responsibility for any damage
arising from virus infections.
 
 

______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email 
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091201/8c772e40/attachment-0002.htm>


More information about the Bldg-sim mailing list