[Bldg-sim] DES Guidance for LEED
Seth P. Spangler
sspangle at rmf.com
Tue Dec 8 11:18:15 PST 2009
Mike,
I have used the exception you noted below on several occasions but in my
opinion your building does not qualify. The exception is for when a
dedicated CEP building is to be modeled. While your building does
contain a central energy pant within it, the building is not a dedicated
CEP building due to the office located above. I assume your building
purchases energy from the plant. A CEP building does not typically
purchase energy from itself which is why the exception was created.
Your office is in effect a satellite building with minimal transmission
losses.
Thanks
Seth Spangler, LEED(r) AP
Project Engineer
RMF Engineering, Inc
Ph: (843) 971-9639 ext:1497
Fax: (843) 971-9641
sspangle at rmf.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Mike
Karpman
Sent: Tuesday, December 08, 2009 1:05 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] DES Guidance for LEED
Hi Everyone,
I'm modeling an office building for LEED that has a DES system. The
central heating and cooling plants are located in the basement of the
building, but also serve other satellite buildings. The DES is owned and
operated by a separate entity (not the building owner).
According to the following excerpt from the DES Guidance for LEED NC 2.2
document dated 3.28.2009 - "Also, the requirements in this document
apply only to the satellite buildings served by the central plant
building; the central plant building itself is treated as an ordinary
building in LEED-NC.", it is our understanding that the building is not
covered by the DES Guidance document (i.e. we are not required to follow
the two step process).
We also think that treating the project as "ordinary building" means
that all central plant equipment should be modeled explicitly as if the
building had a dedicated plant, prorating capacities based on building
sizes.
Does anyone have any experience with this type of situation?
Thanks ahead of time,
Mike Karpman