Hello Dan,
You are correct to use Watts for the SI equation. The counterpart equation for the PTHP (cooling mode, new construction) in the IP version is [12.3 - (0.213 x Cap/1000)], but is expressed as EER (not COP.) COP's are expressed for heating mode as [3.2 - (0.026 x Cap/1000)]. That lower coefficient (0.026) softens the Cap/1000 value, when Cap is in Btu/h.
LOD
===========================
Larry O. Degelman, P.E.
Professor Emeritus of Architecture
Texas A&M University
===========================
From: Dan Jestico
Sent: Tuesday, December 01, 2009 10:34 AM
To: Bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] ASHRAE 90.1-2004 Packaged Terminal Heat Pump Efficiencies
Afternoon all,
We're trying to obtain the minimum CoP for a Packaged Terminal Heat Pump in cooling mode for a new construction using table 6.8.1D in ASHRAE 90.1-2004 (SI edition) and the formula is proving to be somewhat confusing. In the SI edition it is described as
[3.60 - (0.213 x Cap/1000)]
Is this the same equation as listed in the imperial edition of 90.1-2004? If the max. unit capacity of 4.4kW is converted to Btu/hr (approx 15024 Btu/hr, as per note c) and input to the formula, the minimum CoP is only 0.4, which seems very low. However, if I use the value in Watts in the equation, the minimum CoP comes out as a much more reasonable 2.66.
I can't seem to find any addenda on ASHRAE's website or additional guidance on this matter and would very much appreciate any guidance you can provide.
Many thanks for your help.
Dan.
DAN JESTICO
HILSON MORAN
Members of the Italian, Emirates, U.K. and U.S. Green Building Councils
Direct Dial: +44 (0)20 7940 8884
Mobile:
London: +44 (0)7595 106 614
+44 (0)20 7940 8888
www.hilsonmoran.com
Please consider the environment before printing this email.
Registered No: 1233447 England. Registered Office: One Discovery Place, Columbus Drive, Southwood West, Farnborough, Hampshire GU14 0NZ
This message is for the named person(s) use only and may contain confidential, proprietary or legally privileged information. No confidentiality or privilege is waived or lost by erroneous transmission. If you receive this message in error, please immediately delete it and all copies of it from your system, destroy any hard copies of it and notify the sender. You must not, directly or indirectly, use, disclose, distribute, print, or copy any part of this message if you are not the intended recipient. Hilson Moran Partnership Ltd reserves the right to monitor all email communications through its networks. Any views expressed in this message are those of the sender, except where the message specifically states them to be the views of Hilson Moran Partnership Ltd. All transmissions are checked for viruses but all recipients are advised to undertake their own virus checks as Hilson Moran Partnership Ltd will not take responsibility for any damage arising from virus infections.
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email
______________________________________________________________________
--------------------------------------------------------------------------------
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091201/eb4f4d96/attachment.htm>
More information about the Bldg-sim
mailing list