You are fortunate that the explanation worked. I used a very
similarly worded explanation for a project I submitted and the
reviewer didn't go for it. "Inconsistency" seems to be the keyword
for the review process.
At 03:31 PM 8/21/2009, James V. Dirkes II, PE wrote:
>Dear Cramer,
>
>A recent LEED Silver project used this explanation:
>
>"Process load is comprised of receptacles and elevators only, and
>accounts for slightly less than 17% of the total energy cost. The
>receptacle load is assumed to be 0.75 W/sf throughout, which is
>consistent with ASHRAE 90.1 and reflects the tenants' concern for
>efficient office equipment. The receptacle loads also use diversity
>factors that roughly parallel occupancy. The elevator energy is
>derived using actual KW and a diversity schedule that reflects
>normal usage patterns.
>The Diversity schedules are shown on the accompanying updated "HVAC
>Data Summary". These values are based on actual, designed peak
>energy use and appropriate diversity. Therefore, even though
>somewhat lower than 25% of the total energy cost, we are confident
>that they reflect the actual situation adequately and should be
>considered acceptable."
>
>
>The Building Performance Team
>James V. Dirkes II, P.E., LEED AP
>1631 Acacia Drive NW
>Grand Rapids, MI 49504
>616 450 8653<?xml:namespace prefix = o ns =
>"urn:schemas-microsoft-com:office:office" />
>
>
>
>
>
>----------
>From: bldg-sim-bounces at lists.onebuilding.org
>[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Cramer Silkworth
>Sent: Friday, August 21, 2009 1:27 PM
>To: bldg-sim at lists.onebuilding.org
>Subject: [Bldg-sim] leed & process loads
>
>Hi All,
>
>I'm working up a detailed breakdown for process loads in a LEED
>model, to justify using less than 25% of total. I'm wondering what
>other people have gotten down to. If you've submitted with lower
>than 25%, how low did you get, and how detailed was your analysis
>supporting it? I've got computers and other electronic equipment,
>task lighting, and I'm working on the elevator. Anything I'm
>missing? The building is ~50,000 sf, mostly office, but also a
>workout area (I'm accounting for treadmills but nothing else draws any power).
>
>Thanks,
>Cramer
>--
>J. Cramer Silkworth
>Transsolar Climate Engineering
>Technical consulting for energy efficiency and environmental quality
>in buildings.
>134 Spring Street, Suite 601
>New York, NY 10012
>212-219-2255
><mailto:silkworth at transsolar.com>silkworth at transsolar.com
>
>
>
>__________ Information from ESET NOD32 Antivirus, version of virus
>signature database 4358 (20090822) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
><http://www.eset.com>http://www.eset.com
>_______________________________________________
>Bldg-sim mailing list
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>To unsubscribe from this mailing list send a blank message to
>BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>__________ Information from ESET NOD32 Antivirus, version of virus
>signature database 4358 (20090822) __________
>
>The message was checked by ESET NOD32 Antivirus.
>
>http://www.eset.com
Chris Jones
14 Oneida Avenue
Toronto, ON M5J 2E3.
Tel. 416-203-7465
Fax. 416-946-1005
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090822/6fbb87c6/attachment-0001.htm>
More information about the Bldg-sim
mailing list