[Bldg-sim] 62.1 Net Occupiable Area
Alan Jackson
Alan.Jackson at burohappold.com
Wed Apr 15 14:00:00 PDT 2009
Gregg
There is usually a determination that needs to be made between inactive
storage rooms and active storage rooms. You are correct in that if a
storage room is not intended to be occupied by definition than it does
not require OA. Important also is often small storage rooms may contain
noxious chemicals for cleaning that fall under completely different
criteria.
However, with regards to 62.1, the calculation allows rooms that are not
in any way critical spaces (high Evz) to be removed. I would imagine
that if you do decide to provide ventilation to an inactive storage room
it would not be considered your critical space, and therefore is
irrelevant to the calculation.
Alan Jackson, LEED(r) A.P.
Senior Mechanical Engineer
Buro Happold Consulting Engineers, PC
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Gregg
Liddick
Sent: Thursday, April 09, 2009 9:46 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] 62.1 Net Occupiable Area
I was determining flow rates for a building when I ran across this
conundrum concerning outdoor air requirements in storage rooms.
Hopefully someone can help me out.
Vbz=RpPz + RaAz
Where Az is the "zone floor area: the net occupiable floor area of the
zone" and Ra is the "outdoor airflow rate required per unit area as
determined from Table 6-1". Mechanical rooms have a value for Ra listed
in Table 6.1.
However, occupiable space is defined under "Definitions" as "an enclosed
space intended for human activities, excluding those spaces intended
primarily for other purposes, such as storage rooms and equipment rooms,
that are only occupied occasionally and for short periods of time".
Does this mean that there are no outdoor air flow requirements for
storage rooms? If so, why is there a value listed for the outdoor
airflow rate required per unit area?
Thanks,
Gregg Liddick
This message has been scanned by MailController
<http://www.mailcontroller.altohiway.com/> .
Click here
<https://www.mailcontroller.altohiway.com/sr/jPOfn0TtXpPTndxI!oX7UiM+xhr
vJ3fWN3+TBOHyXsU9a3RKAUDkvJSav83zxZ6EMsbklhvLGBNICd5VsZuQpQ==> to
report this email as spam.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090415/98017971/attachment.htm>
More information about the Bldg-sim
mailing list