I have noticed this too.  The constant volume exhaust fan merely means that
the fan runs constantly, but may not draw air through the space (read the
help file on this, it's more eloquent than I am).

What I have done to remedy this issue using other system types is specify
that the system fan operates as a variable volume fan, with the fan curve
being linear.  This will allow the fan to modulate down to the required
exhaust airflow.  If you look at the help files for "SUPPLY-KW/FLOW" it
shows the fan curves for variable speed fans, cycling fans, discharge, etc.
So this is the way that the program models cycling fans already, and you can
use it to your advantage with the exhaust airflow piece.

Hope this works!

--
Karen


On Tue, Sep 23, 2008 at 12:11 PM, Yuvaraj Saravanan <
Yuvaraj.Saravanan at arup.com> wrote:

>  Hi All,
> I am trying to model a residential unit served by a Fan coil unit (FCU). It
> has a separate outside air fan and exhaust fan operating 24/7. The fan coil
> unit is available to operate for all hours but should operate intermittently
> depending on the room load.
>
> I tried modeling this by selecting a 4-pipe FCU and specified the exhaust
> and outside air at the thermal zone level. I made the FCU to operate
> intermittently by making the "Fan on mode" to be intermittent. By doing
> this, what I observed in the hourly report was:
>
> 1. FCU unit cycles intermittently as intended.
> 2. Exhaust fan operates continuously (24/7) (with the specified cfm) as
> intended.
> 3. However, the outside air cycles per the FCU.
> •If the FCU is off, then OA cfm is zero
> •If FCU supply air cfm < the OSA cfm specified at the zone level, then
> hourly OSA cfm matches the FCU supply air cfm •If FCU supply air cfm > the
> OSA cfm specified at the zone level, then hourly OSA cfm matches the cfm
> specified at the zone level.
>
> As mentioned before, I want my outside air to operate continuously with
> constant flow-rate. Can anyone suggest me a way to model this system?
>
> Thanks in advance for your help!
> Regards,
> Yuvaraj
>
> ______________________________________________
> Yuvaraj Saravanan, PE
> Engineer
>
> Arup
> 12777 West Jefferson Boulevard Suite 200
> Los Angeles CA 90066
> tel:    1 310 578 4400
> dir:    1 310 578 4521
> fax:    1 310 577 7011
> internal freecall: x20521
> yuvaraj.saravanan at arup.com
> ***www.arup.com*
>
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup  business
> systems are scanned for acceptability of content and viruses
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080923/5b320156/attachment-0001.htm>


More information about the Bldg-sim mailing list