[Bldg-sim] Glass center-of-glass to assembly U-Value?
karen mozes
kmozes at gmail.com
Mon Sep 22 09:47:10 PDT 2008
Hi,
Chapter 31 (Fenestration) of Ashrae handbook fundamentals has average
overall U-values for different frame types (weighted average for a frane of
2.5" I believe, which also includes the glassedge effect). Accurate U-values
need to be calculated using NFRC standards, using approved software (in the
US this is LBNL Windows and Therm).
I am not aware of a visible light transmittance requirement, but the lower
the transmittance, the less daylighting benefits you will get, as you know,
so there are no energy benefits for having a low Vt. Glass manufacturers
work hard to keep light transmittances high and SHGC low.
Hope this helps
Kind regards,
Karen
(Arup Facades)
On Mon, Sep 22, 2008 at 12:06 PM, Josh Greenfield <
JGreenfield at primerachicago.com> wrote:
> Does anyone have any rules of thumb on a quick/easy approximation for
> taking a Center-of-Glass U-value and converting it to an Assembly U-value
> based on industry standard assembly constructions? I know this depends on a
> lot of variables, like frame material and conductance, and the size of the
> overall glass assembly, etc., but I'm just looking for a quick estimate on
> performance reduction for comparisons to other window types for a particular
> building.
>
>
>
> Also, is there an ASHRAE 90.1-2004 Baseline glass Visible Light
> Transmittance (VLT)?
>
>
>
> Josh Greenfield, PE, LEED AP
> Senior Associate
> Primera Engineers, Ltd.
> 100 S. Wacker Drive, Suite 700
> Chicago, IL 60606
> 312.606.0910 Main
> 312.242.6392 Direct
> 312.606.0415 Fax
> jgreenfield at primerachicago.com
> http://www.primerachicago.com
>
> Be Green...please consider the environment before printing this email.
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Karen Elisabeth Mozes
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080922/88dcdae4/attachment.htm>
More information about the Bldg-sim
mailing list