[Bldg-sim] Building Shell Problem

Dan Russell danr at engineeringinc.com
Mon Sep 8 07:29:55 PDT 2008


For some reason eQUEST won't allow a Restore Default on this particular
item.  So, you have to delete the AREA reference in the .inp file.  

 

If you open the file and search for the space name that is giving you
troubles, find the line that defines AREA.  Delete this entire line and
the program will revert to the calculated area based on the polygon
definition.

 

Thanks,

 

 Dan Russell, EIT 

 

 

 

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Christopher
Sturdivant
Sent: Monday, September 08, 2008 7:38 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Building Shell Problem

 

Hello,

I have run into a difficult situation in equest.  I decided one day to
go into the building shell and manually enter in the area and then it
gave me errors that if the polygon is input then area cannot be used.
So I went in and tried to change it back to the way it was and it keeps
giving me errors.  Is there a way to alleviate this?

Thanks!!

 

 

Christopher Sturdivant

Design Engineer-Mechanical

 

RMF Engineering, Inc.

Ph: 843-971-9639 ext. 110

Fax: 843-971-9641

csturdiv at rmf.com

 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080908/d7387029/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 7994 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080908/d7387029/attachment.jpeg>


More information about the Bldg-sim mailing list