[Bldg-sim] Green Facade

Ulrik Welle-Strand Horn ulrik.horn at silpainc.com
Tue Oct 21 11:31:27 PDT 2008


Hi Patrick,

In general, green walls can be modeled as a wall with a shading device. Make
sure the shading is very close to the wall. There will be very little
insulating effect from the leaves, and they are not an efficient wind
breakers. Make sure the vegetation for the plant type specified is dense
enough to shade the entire wall. Else, you might want to shade only parts of
the wall proportionally to the density of the vegetation. Make sure you are
not shading the windows, as these are usually kept free from vegetation.

Also, you must pay attention to whether the wall itself is significantly
altered due to the vegetation. The most common green walls have the plant
rooted in the ground with only minor attachment points on the wall. In this
case you model the wall like any other wall. However, sometimes plants are
grown on the wall itself, with small shelves filled with earth. If this is
the case, you must make sure you model the areas filled with earth if they
occupy significant parts of the wall.

Lastly, the attachment points for the plant may in some instances have
significant effects on the thermal performance of the wall. Make sure you
incorporate this in your model if it applies to your building.

Let me know if you have any other questions.

Sincerely yours,


*Ulrik Welle-Strand Horn *
Sustainability Engineer

*Silpa Inc.*
*s* i m p l e  .  *s* c i e n t i f i c  .  *s* u s t a i n a b l e
AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com

India: +91.90080.96083




On Tue, Oct 21, 2008 at 10:14 PM, Patrick Wilkinson <
patrick.wilkinson at ibece.net> wrote:

>  Has anyone tried to model an external green wall? If so, any help on how
> to do this would be great.
>
>
>
> Thanks
>
>
>
> *Patrick Wilkinson**,** **B.Sc. ENG,** **LEED(R) AP**
> Advanced Technology Group**
> *
>
> 14130 Riverside Drive Suite 201
> Sherman Oaks, CA 91423
> p:   (818) 377-8220 ext. 240
> f:    (818) 377-8230
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> This e-mail message, including any attachments, is for the sole use of the
> intended recipient(s) and may contain confidential and privileged
> information. Any unauthorized review, use, disclosure, or distribution is
> prohibited. If you are not the intended recipient, please contact the sender
> by reply e-mail and destroy all copies of the original message
>
>
>
> .
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081022/4321a2cb/attachment.htm>


More information about the Bldg-sim mailing list