[Bldg-sim] WSHP
Brian Fountain
bfountain at greensim.com
Mon Oct 20 07:28:16 PDT 2008
Ensure your fan operation is consistently "constant". If fans are
"intermittent", OA is only introduced when the fan is on -- and the fan
run hours are likely different between the two system types depending on
capacity & control -- which will skew your results.
Chris Mullinax wrote:
>
> On three or four occasions I have used equest to compare traditional,
> small split systems (three to five ton) to a water source heat pump
> system in the same building. The WSHP system uses a cooling tower and
> a small boiler.
>
>
>
> I tried to make everything else identical by creating the first model
> and saving a copy of that model and changing the HVAC type from split
> system to WSHP.
>
>
>
> On every occasion, split systems end up using significantly less
> energy than water source heat pumps systems.
>
> The WSHPs are typically 16 SEER, the Splits 13 SEER.
>
>
>
>
>
> I know there is additional energy associated with pumps and cooling
> towers. Is this a typical result?
>
> It seems I've heard a lot of high about the efficiency of water source
> heat pumps.
>
>
>
>
>
> Thanks,
>
> Chris Mullinax, P.E. LEED AP
>
>
>
> pn: 770-387-1334
>
> fx: 770-387-1383
>
> chris at mullinaxsolutions.com <mailto:chris at mullinaxsolutions.com>
>
> www.mullinaxsolutions.com <http://www.mullinaxsolutions.com>
>
>
>
>
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
> ------------------------------------------------------------------------
>
> No virus found in this incoming message.
> Checked by AVG.
> Version: 7.5.549 / Virus Database: 270.8.1/1732 - Release Date: 10/18/2008 6:01 PM
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081020/a8ff6514/attachment.htm>
More information about the Bldg-sim
mailing list