[Bldg-sim] Amount of heat recovered for an electric heat recoverychiller
Jeff P. Waller
jwaller at cambridge-eng.com
Fri Oct 10 07:38:00 PDT 2008
If the condenser and recovery loop are in series, it is probably done to
protect the system from having the condensing loop oversized. I had to
address this concern in the supermarket industry a number of years ago.
A particular supermarket chain purchased the same model of heat recovery
for every store regardless of the size and amount of refrigeration in
each store. This resulted in some smaller stores having an oversized
heat recovery system. This is primarily a concern for part load
operation.
If the refrigerant changes to liquid before it hits the condenser, the
condenser becomes a refrigerant tank. What effectively happens is that
the system's volume of refrigerant (as liquid phase in the condenser)
starves the evaporators. In the case I spoke of, the maintenance people
then added refrigerant to the system which worked until the system
neared design load again and then the system tripped on high head. This
produced an endless cycle of adding/removing refrigerant until we had
the owner resize the heat recovery loop.
And, our standard as refrigeration engineers, was to size the heat
recovery system for no more than 50% credit for this very reason.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of
Aaron.Etzkorn at tac.com
Sent: Friday, October 10, 2008 9:04 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Amount of heat recovered for an electric heat
recoverychiller
All:
Does anyone know why there is a maximum limit of around 50% of the
available heat rejection from the chiller condenser that can be rejected
to a heat recovery loop.
Can this be overcome, or is it a default for that chiller type?
Thanks,
Aaron Etzkorn, EIT
Engineer I
TAC
16011 College Blvd, Suite 212
Lenexa, KS 66219
Direct: +1 (913) 469-0203
Fax: +1 (913) 469-0206
Mobile: +1 (913) 620-3291
Email: Aaron.Etzkorn at tac.com
Web: www.tac.com <http://www.tac.com/>
Notice: This email message, together with any attachments, contains
information of TAC, which may be confidential, proprietary, copyrighted
and/or legally privileged. This email is intended solely for the use of
the individual or entity named on the message. If you are not the
intended recipient, and have received this message in error, please
immediately return by email and then delete it.
P Please consider the environment before printing this e-mail. Thank
you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081010/ce08268a/attachment.htm>
More information about the Bldg-sim
mailing list