[Bldg-sim] LEED/Appendix G HVAC Baseline Systems
Ulrik Welle-Strand Horn
ulrik.horn at silpainc.com
Sun Nov 2 19:25:11 PST 2008
Dear Mr. Rick Routh,
You will have to assign one system type 3 to every zone in your building.
System type 3, as you point out, are single zone units, meaning they can
only respond to one thermostat input. However, in ASHRAE 90.1 User's Manual,
2004 on page G-23 they say that "the baseline building HVAC system is a
rooftop packaged system serving each thermal zone (or thermal block)." This
allows you to group similar zones in your proposed building together, and
you can assign your System type 3 to each block instead, speeding up the
calculations for your model. However, your thermal blocks must be specified
identically in your proposed and baseline building. Example G-H on page G-27
in the same User's Manual highlights this point.
For information on thermal blocks and how they are modeled in your proposed
building, refer to ASHRAE 90.1 (the standard, not the user's manual), p 173,
table G3.1 - 7.
I hope this clarifies your question, if not, feel free to contact me.
Sincerely yours,
*Ulrik Welle-Strand Horn *
Sustainability Engineer
*Silpa Inc.*
*s* i m p l e . *s* c i e n t i f i c . *s* u s t a i n a b l e
AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com
India: +91.90080.96083
On Sun, Nov 2, 2008 at 11:06 PM, Routh Consulting Engineers <
routhconsultingengineers at charter.net> wrote:
> I am modeling a new building applying for LEED certification and want to
> make sure I'm using the right Appendix G baseline HVAC system
> configuration. The proposed design has three gas/electric rooftop packaged
> HVAC units, each with VVT dampers for subzoning, 6 to 12 subzones per
> system, all zones are defined at the stage of design development we're at. I
> believe I need Appendix G system type 3, gas/electric single zone units for
> my baseline, but do I use the same three HVAC unit configuration and
> assign the same eQUEST spaces/zones to the corresponding systems, or do I
> use a separate HVAC system for each space/zone? Thanks in advance for any
> replies.
>
> Rick Routh
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081103/47ea1da3/attachment-0001.htm>
More information about the Bldg-sim
mailing list