90.1 climate zoneHello Yuvaraj:
Mexico City climate is a 3A classification and therefore there is no requirement for an economizer system.
The annual average temperature is 64F, and the annual rainfall is 25.7 inches. Using the formula on page 112 of 90.1-2007, the precipitation criteria is 19.58". Since the 25.7" does not fall below 19.58", it fails in the criteria for dry zone B. It also fails to meet the marine criteria (zone C), and therefore it classifies as moist (zone A).
Regards,
Larry
===================================
Larry O. Degelman, P.E. ldegelman at suddenlink.net
Professor Emeritus of Architecture
Texas A&M University
===================================
From: Yuvaraj Saravanan
Sent: Wednesday, November 26, 2008 2:10 PM
To: bldg-rate at lists.onebuilding.org ; equest-users at lists.onebuilding.org ; bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] 90.1 climate zone
Hi All,
I am trying to do an energy modeling using ASHRAE 90.1 performance rating method for a building in Mexico City, Mexico. I am trying to figure out where Mexico City would fall under for the climate zone. Table B-3 tells me the Zone number but it does not tell me the Climate Type (A, B or C). So, I followed the Table B-4. This does not classify between A or B for zone 3 based on the degree days. I also went through Appendix B2 (Major climate type definitions) page 109. I was able to climate that it is not Climate Zone type C. But in order to verify whether I am in B, I need to know the annual precipitation. Where do I get this value from? Will it be in ASHRAE or any other standards? I searched in the website and I am getting different values for Mexico city precipitation. Depending on this I would either fall in A or B. Would like to follow some standards rather than searching in the website.
I am writing this story because I need to figure out whether my baseline would require an economizer or not. Zone-3A does not require an economizer where as Zone-3B does.
Any guidance will be appreciated.
Thanks,
Yuvaraj
______________________________________________
Yuvaraj Saravanan, PE
Engineer
Arup
12777 West Jefferson Boulevard Suite 200
Los Angeles CA 90066
tel: 1 310 578 4400
dir: 1 310 578 4521
fax: 1 310 577 7011
internal freecall: x20521
yuvaraj.saravanan at arup.com
www.arup.com
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
--------------------------------------------------------------------------------
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
--------------------------------------------------------------------------------
No virus found in this incoming message.
Checked by AVG.
Version: 7.5.549 / Virus Database: 270.9.10/1813 - Release Date: 11/26/2008 8:53 AM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081126/16bea5af/attachment.htm>
More information about the Bldg-sim
mailing list