[Bldg-sim] Dormitory LPD
Bishop, Bill
bbishop at PathfinderEngineers.com
Thu Nov 20 13:30:37 PST 2008
Tim,
Table G3.1, No. 6(d) states: "Lighting system power shall include all
lighting system components shown or provided for on the plans (including
lamps and ballasts and task and furniture-mounted fixtures). Exception:
For multifamily living units, hotel/motel guest rooms, and other spaces
in which lighting systems are connected via receptacles and are not
shown or provided for on building plans, assume identical lighting power
for the proposed and baseline designs in the simulations, but exclude
these loads when calculating the baseline building performance and
proposed building performance." [Emphasis in original.]
The way I would implement this is to assign the same W/ft2 lighting to
all dorm rooms on a different meter in both the baseline and proposed
designs. Then I would subtract the kWh of that meter from the building
performance. You could still show lighting savings if you do the
space-by-space method for both designs (assuming the lighting in your
corridors and common areas is efficient).
Regards,
Bill
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers LLP
Mechanical Engineer
3300 Monroe Ave., Suite 306
Rochester, NY 14618
TEL (585) 218-0730 Ext. 114
FAX (585) 218-0737
bbishop at pathfinderengineers.com
www.pathfinderengineers.com
P Please consider the environment before printing this email
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Howe,
Timothy
Sent: Thursday, November 20, 2008 4:10 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Dormitory LPD
Sim-users,
I have a dormitory with something like 3/4 dorms and the rest support
areas.
My question is:
ASHRAE 90.1-2004 calls for in the building wide approach for lpd to be
1.0 w/sf for dorms.
Now if there are wall switched fixed lights called for on the electrical
lighting plans in the dorm rooms but have only a small w/sf
contribution, can I really do a building wide lpd calc and claim the
savings shown on the plans??
Any suggestions??
Thanks.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081120/92cff8d2/attachment.htm>
More information about the Bldg-sim
mailing list