[Bldg-sim] Exhaust, outside air and infiltration for LEED
Brandon Nichols
bwnichols at gmail.com
Fri Nov 7 12:46:43 PST 2008
My two cents...
The same OSA for baseline vs as-designed makes sense for occupant-required
OSA, such that there is no reward for compromising occupant health to gain
LEED points.
However, that fraction of the fumehood OSA over and above occupancy-required
is *process* OSA, an opportunity where LEED *should *be encouraging
savings. Now I'm not saying they do, just that they *should...*
And after rereading the requirements it shakes out that LEED really doesn't
give credit for reducing process outside air loads, keep the parametric run
in your model -- the local utility may see things differently, and
'recognize you' with a big fat rebate check.
Cheers
Brandon Nichols
BW Nichols PE
Seattle WA
206-228-8707
On Fri, Nov 7, 2008 at 11:53 AM, Michael Tillou <michael.tillou at gmail.com>wrote:
> You are correct that Appendix G requires outside air to be the same for
> both as-designed and baseline models. You would not be able to claim
> savings for reduced ventilation airflow from a more efficient fume
> hood. Similarly you cannot claim credit for reduced ventilation airflow on
> displacement ventilation and UFAD systems.
>
> However I see no reason why you wouldn't be able to claim the fan energy
> savings associated with a more efficient fume hood.
>
> Mike
>
> Michael Tillou, PE, LEED
> Tillou Engineering, LLC
> Williamstown, MA 01267
> P: 413-458-9870 C: 413-652-1087
> ------------------------------
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Bishop, Bill
> *Sent:* Friday, November 07, 2008 9:04 AM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] Exhaust, outside air and infiltration for LEED
>
> The mechanical engineer for a campus laboratory building with 100% OA
> wants to claim energy savings for reduced exhaust from more efficient fume
> hoods. (Established design practice uses hoods with 100 fpm flow – they are
> installing 70 fpm hoods. This reduces peak exhaust from 700 to 490 CFM per
> hood.) My approach has always been to keep outside air, exhaust and
> infiltration flows identical between the proposed and baseline models
> (except for DCV). (This was not easy for this model with proposed VAV and
> baseline constant volume packaged rooftops.)
>
>
>
> Has anybody successfully claimed OA/exhaust/infiltration savings for a LEED
> project?
>
>
>
> Thanks,
>
> Bill
>
>
>
> *William Bishop**, EIT, LEED(R) AP** **|** **Pathfinder Engineers LLP*
>
> Mechanical Engineer
>
>
>
> 3300 Monroe Ave., Suite 306
> Rochester, NY 14618
>
> TEL (585) 218-0730 Ext. 114
> FAX (585) 218-0737
>
> bbishop at pathfinderengineers.com
>
>
>
> www.pathfinderengineers.com
>
> P Please consider the environment before printing this email
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081107/f540f36b/attachment.htm>
More information about the Bldg-sim
mailing list