[Bldg-sim] App G system type 6 story 100,000 sq ft building
Bishop, Bill
bbishop at PathfinderEngineers.com
Fri Nov 7 07:42:03 PST 2008
James,
I'd stick to Table G3.1.1A and use System 8. The wording in the 2004
User's Manual looks like a mistake. The wording in the Standard
90.1-2007 User's Manual, p.G-23, is changed to, "For intermediate-sized
buildings that are 4 or 5 floors and less than 25,000 sq ft or less than
6 floors and between 25,000 and 150,000 sq ft, the baseline building
HVAC system for electric heat is packaged VAV system."
Regards,
Bill
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers LLP
Mechanical Engineer
3300 Monroe Ave., Suite 306
Rochester, NY 14618
TEL (585) 218-0730 Ext. 114
FAX (585) 218-0737
bbishop at pathfinderengineers.com
www.pathfinderengineers.com
P Please consider the environment before printing this email
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James
Hansen
Sent: Friday, November 07, 2008 10:08 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] App G system type 6 story 100,000 sq ft building
I searched thru the archives but couldn't fiind an answer to this.
Why is there a direct conflict in the required Baseline system type
between the App G chart in 90.1 and the wording in the 90.1 user manual?
I have a 6-story building that is 100,000 sq ft. If I read Table
G3.1.1A of 90.1, it says:
"Nonresidential & More than 5 floors OR > 150,000 sq ft", that I should
use System 8 (VAV with PFP boxes).
Even Table G-A in the User Manual says the same thing.
In addition, the requirements for using System 6 say:
"Non residential, 4 or 5 floors or less than 75,000 sq ft OR 5 floors or
less and 75,000 - 150,000 sq ft".
Both of these facts would lead me to believe that anything over 5
stories should be System 8. However, the wording in the User Manual
goes on to say that:
"For intermediate-sized buildings that are 4 or 5 floors and less than
75,000 sq ft or more than 5 floors and between 75,000 and 150,000 sq ft,
the baseline building HVAC system for electric heat is packaged VAV
system."
I've finished modeling the Baseline building with System 8, but now that
I've read the User Manual, it would appear that I am supposed to use
PVAV. I really hope I don't have to go back and change the baseline
system again.
Any thoughts?
Thanks
James Hansen
________________________________
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is
the property of GHT Limited. Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081107/7c583751/attachment.htm>
More information about the Bldg-sim
mailing list