[Bldg-sim] EER to EIR Conversion for LEED Baseline
Kevin Kyte
kkyte at robsonwoese.com
Thu Nov 6 14:00:48 PST 2008
OK, I read it again. Autosize the baseline and run four orientations to obtain the capacities (assuming an average of the four). These capacities will be oversized. I understand. Thank you.
From: Aulbach, John [mailto:jaulbach at nexant.com]
Sent: Thursday, November 06, 2008 4:05 PM
To: Kevin Kyte; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] EER to EIR Conversion for LEED Baseline
Kevin:
I believe it is 15% oversize for cooling and 25% for heating (Page 176 - Appendix G - ASHRAE-90.1-2004 - I don't have 2007 yet). This is aside from fan calculations.
This would apply to either package units or central plant equipment, whichever is specified as baseline.
John R. Aulbach, PE, CEM
Project Manager
Nexant, Inc.
701 West Kimberly Ave., Suite 245
Placentia, CA 92870-6342 USA
Phone: 714-524-4402
Fax: 714-524-4407
email: jaulbach at nexant.com<mailto:jaulbach at nexant.com>
________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Kevin Kyte
Sent: Thursday, November 06, 2008 12:54 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] EER to EIR Conversion for LEED Baseline
All,
When you Calc your EIRs for baseline, do you use design capacities or oversized baseline capacities?
Thank you.
Kevin
________________________________
"This message is for the designated recipient only and may contain privileged, proprietary, or otherwise private information. If you are not the intended recipient, you are hereby notified that any disclosure, copying, distribution, or the taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please notify the sender immediately by e-mail and delete the original message."
________________________________________________________________________
This Email has been scanned for all viruses by PAETEC Email Scanning Services, utilizing MessageLabs proprietary SkyScan infrastructure. For more information on a proactive anti-virus service working around the clock, around the globe, visit http://www.paetec.com.
________________________________________________________________________
________________________________
"This message is for the designated recipient only and may contain privileged, proprietary, or otherwise private information. If you are not the intended recipient, you are hereby notified that any disclosure, copying, distribution, or the taking of any action in reliance on the contents of this information is strictly prohibited. If you have received this transmission in error, please notify the sender immediately by e-mail and delete the original message."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081106/40a44f81/attachment.htm>
More information about the Bldg-sim
mailing list