[Bldg-sim] Baseline System for Appendix G

Arvinder Dang Arvinder.Dang at som.com
Thu Nov 6 10:29:19 PST 2008


Can someone please provide input regarding what would be the correct Appendix G baseline system for a 4 storied building > 150,000 sf which has a chilled water system for cooling and uses electric series fan powered boxes for perimeter heating. There is a gas fired dedicated outside air unit that supplies air to all the Air handling Units. The gas fired OA units use about 35% of the total heating energy for the building. The rest 65% is from the perimeter boxes. The total heating utility cost for gas is very small ($6500) compared to the total building utility cost ($270,500).

We intend to submit this project for LEED and are struggling since the choice of the base system significantly changes the performance of the building. We have implemented a number of energy saving measures in the design like better insulation in walls and roof, high performance glass, daylight sensors, occupancy controls, reduced lighting power density, heat recovery, water side economizer. Our building saves about 15%energy compared to the baseline system when using System 7 as the baseline. However in terms of Utility this imposes a major penalty and barely meets the baseline Utility Cost when compared to a hydronic system i.e., System 7.
When the baseline is modeled as System 8 we can the 14% Utility Cost savings.

Has someone modeled a system similar to this before and submitted it for LEED. What would be the correct choice for the baseline system.
There is note on page 176 which states" Where attributes make a building eligible for more than one building system type, use the predominant condition to determine the system type for the entire building. "

We think this exception would apply to our design since most of our heating is electric and System 8 would be the right system to use.

One option around this is to change our Outside air units as electric and then there would be no question regarding the base system as it would be electric System 8. However we do not think this is the right design approach since the proposed design would have more utility cost than the current scenario and meet LEED 14% requirements.

There was a discussion regarding this a few days back on the forum and there was a mention of a CIR dated 9/27/2006. Would this apply to our case?

I know there are a number of experienced professionals on this forum who have been involved with the LEED energy and atmosphere credits documentation evaluation for different LEED projects for this credit. I would appreciate your insight.

Please advise.

Thanks
ARVINDER DANG, LEED(r) AP
SUSTAINABILITY SPECIALIST


From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rosenberg, Michael I
Sent: Monday, November 03, 2008 10:43 AM
To: James Hansen; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Fossil/Electric hybrid system under 90.1 App G

Yes, you are correct. Appendix G requires that if you have any gas heat in your Proposed building, the baseline system would use gas heat. However, if this is for a LEED submittal, you may want to do a little research on relevant CIR's since USGBC has interpreted this a little differently than was intended by Appendix G.

_________________________

Michael Rosenberg
Senior Commercial Buildings Energy Analyst
ENERGY & ENVIRONMENT DIRECTORATE

Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960
michael.rosenberg at pnl.gov
www.pnl.gov


________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James Hansen
Sent: Monday, November 03, 2008 8:32 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Fossil/Electric hybrid system under 90.1 App G
I can't seem to find reference to this in the 90.1 User Manual.

In Appendix G, Table G3.1.1A, there is a reference to a Fossil/Electric hybrid for determining Baseline system type.  Is this a system that, for example, might have a gas-fired RTU with electric VAV boxes?

In other words, if there is ANY gas heat in your Proposed building, your Baseline building would have to automatically default to a fuel furnace or gas-fired hot water heating system, correct?

Thanks,

GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA  22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com<http://www.ghtltd.com/>
size=2 width="100%" align=center>
The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com<mailto:ght at ghtltd.com>, and destroy this communication and all copies thereof, including all attachments.  Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081106/fdbe48d1/attachment.htm>


More information about the Bldg-sim mailing list