[Bldg-sim] Fossil/Electric hybrid system under 90.1 App G
Paul Riemer
Paul.Riemer at dunhameng.com
Mon Nov 3 09:20:49 PST 2008
I believe the/a CIR that Mr. Rosenberg is referring to is an NC v 2.2 CIR submitted 9/27/06 and answered on 10/23/06 that hinges on the gas being preheat.
I have not read the CIR Mr. Dec mentioned although that seems fascinating too.
Paul Riemer
________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rosenberg, Michael I
Sent: Monday, November 03, 2008 10:43 AM
To: James Hansen; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Fossil/Electric hybrid system under 90.1 App G
Yes, you are correct. Appendix G requires that if you have any gas heat in your Proposed building, the baseline system would use gas heat. However, if this is for a LEED submittal, you may want to do a little research on relevant CIR's since USGBC has interpreted this a little differently than was intended by Appendix G.
_________________________
Michael Rosenberg
Senior Commercial Buildings Energy Analyst
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960
michael.rosenberg at pnl.gov
www.pnl.gov
________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James Hansen
Sent: Monday, November 03, 2008 8:32 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Fossil/Electric hybrid system under 90.1 App G
I can't seem to find reference to this in the 90.1 User Manual.
In Appendix G, Table G3.1.1A, there is a reference to a Fossil/Electric hybrid for determining Baseline system type. Is this a system that, for example, might have a gas-fired RTU with electric VAV boxes?
In other words, if there is ANY gas heat in your Proposed building, your Baseline building would have to automatically default to a fuel furnace or gas-fired hot water heating system, correct?
Thanks,
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com<http://console.mxlogic.com/redir/?IKnspLtASC--ZtVVMS028AVDPgVv3tPtPp0Z0ynF9kKgGT2TQ1hYGjFRougrAuxa17w09J5xxZASyCC-epK-qekPry9I5-Aq83iScDE4iZ9aCBQQg2ZqkAvwQvZFNBoQg4ON2cA3h1gJivGCy1K27Nd41EVLO9Ew45Bzh04zs_3VU3zq9J4SC--ZtVVUSJ3iidPW>
________________________________
The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com<mailto:ght at ghtltd.com>, and destroy this communication and all copies thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081103/56bc9619/attachment.htm>
More information about the Bldg-sim
mailing list