[Bldg-sim] chiller EIR curve
W. Peter Anderson
panderson at jpengineer.com
Fri May 23 14:25:28 PDT 2008
I have not spent much time researching the eQuest EIR curve origins, but I have spent years performing chiller ratings and analyzing centrifgual chiller part load curves under many circumstances.
In my opinion, the CVHE curve is much more representative of what the energy use will be for (1) chiller operating, than the eQuest curve. The nature of centrifugal chiller is, below 25% loading the kW/ton increases. Basically, system inefficiencies, which are relatively minor compared to power of compression at higher loads, are a bigger percentage of work input (kW) at low loads.
If you have mulitple chillers, more information is needed to make a determination of what your part load efficiency would be.
It would be good to get feedback from someone more familiar with eQuest EIR.
SEER is calculated differently than water cooled chiller performance, so that could be a source for differences as well.
I hope this helps,
Regards,
----- Original Message -----
From: Xu, Xiaowei
To: bldg-sim at lists.onebuilding.org
Sent: Friday, May 23, 2008 4:06 PM
Subject: [Bldg-sim] chiller EIR curve
Hi,
I have a question about the chiller EIR curve in eQUEST. In the attachment, there are two curves of chiller EIR. One is the kWH/Ton curve from chiller manufacture. One the normalized EIR curve from eQUEST default. These two curves showed quite big difference when the chiller PLR drops to 30% or lower.
In my simulation, I used manufacturer data and this equation to calculate the EIR, and then normalized the EIR to get the curve.
Cooling EIR = 0.941 * (1/(SEER/3.413))
Because about 20% of the chiller hours ran at less 20% of PLR, using two different curves (calculated manufacturer curve and eQUEST default curve) caused huge difference of chiller electricity consumption. So my question is which curve is right for the chiller performance? Thank you very much.
Xiaowei Xu
Engineer
FLACK + KURTZ
475 Fifth Avenue
New York, NY 10017
http://www.flackandkurtz.com
212.532.9600 Main
212.951.2662 Direct
212.689.7489 Fax
xiaowei.xu at ny.fk.com
Ensuring that today's built environment preserves the natural environment in which we live.
This e-mail may contain confidential and/or privileged information. If you are not the intended recipient (or have received this e-mail in error) please notify the sender immediately and destroy this e-mail. Any unauthorized copying, disclosure or distribution of the material in this email is strictly forbidden.
------------------------------------------------------------------------------
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080523/75df36df/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 837 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080523/75df36df/attachment.gif>
More information about the Bldg-sim
mailing list