[Bldg-sim] DOE2 User Input Expressions

Scott Criswell scott.criswell at doe2.com
Fri May 23 12:00:35 PDT 2008


Brian's suggestion is a good one, but requires the use of global parameters.

This correction however will fit directly into your particular project:

if (#L("LIGHTING-SCHEDUL",0) ==
    #SI("Classroom InstLt Sch","SPACE","LIGHTING-SCHEDUL"))
then  1.2
else  0
endif

Things to note:
- DOE-2 keyword names are limited to 16 characters, hence the use of 
"LIGHTING-SCHEDUL" in place of your "LIGHTING-SCHEDULE"
- LIGHTING-SCHEDUL is actually an array of 5 individual schedule 
assignments, so we specify the optional second #L() argument of "0" 
indicating that we are interested in retrieving the first (0-based, not 
1-based) element in the list (which is the default).
- Use of the #SI() function so that we are comparing a symbol table 
index to another symbol table index.


Brian Fountain wrote:
> try this:
>
>   PEOPLE-SCHEDULE  =
> {if (#PA("Schedules") == "Title24")
>                        then #SI("T24 DAYTIME 
> OCC","SPACE","PEOPLE-SCHEDULE")
>                        else #SI("Rink Occ Sch","SPACE","PEOPLE-SCHEDULE")
>                       endif}
>
> Steve Mignogna wrote:
>> All-
>>
>> I'm looking to use "if statements" within DOE2.  For example, I'm 
>> trying to input a specific LPD based on the type of lighting schedule 
>> that is specified.  Ideally, I would like to couple multiple if 
>> statements together but I can't even get this one to work:
>>
>> {if(#L("LIGHTING-SCHEDULE")=Classroom InstLt Sch)
>> then 1.2
>> else 0
>> endif}
>>
>> Any ideas on how this could work?
>>
>> Thanks,
>>
>> -- 
>> Steve Mignogna
>> Atelier Ten
>> ------------------------------------------------------------------------
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to 
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>   
>> ------------------------------------------------------------------------
>>
>> No virus found in this incoming message.
>> Checked by AVG. Version: 7.5.524 / Virus Database: 269.24.0/1462 - 
>> Release Date: 5/23/2008 7:20 AM
>>   
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to 
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>


More information about the Bldg-sim mailing list