[Bldg-sim] Vertical butt joint glazing - thermal bridging

Vikram Sami VSami at lasarchitect.com
Thu May 15 06:46:10 PDT 2008


Neeraj is correct regarding the size (and aspect ratio) of the pane making a difference. Essentially - the ratio of perimeter to area s a bid riving factor. I think you could arrive at the overall U-value using Window 5.2 by LBNL - it allows for different window sizes, and you can customize your frame conductance.
 
With regards to frame conductance, most manufacturers will give you those numbers if you ask them - they should have it for butt glazed systems too (I assume you mean structural silicone glazing where the frame is behind the glass). 
 
 
 
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366

LORD, AECK & SARGENT ARCHITECTURE
Responsive Design · Technological Expertise · Exceptional Service
www.lordaecksargent.com 

________________________________

From: bldg-sim-bounces at lists.onebuilding.org on behalf of Neeraj Kapoor
Sent: Thu 5/15/2008 00:29
To: Chris Jones; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Vertical butt joint glazing - thermal bridging



Hello Chris,

Seems like you would need to (appropriately) average out "edge of
glass"
and "center of glass" u-values. This may be a function of the size of
the glass plane, i.e. a large glass plane will have predominantly
"center of glass" u-value characteristics rather than "edge of glass".
My question back to the bldg-sim(ers) will be -- are there any studies
/
empirical data drawing relationship between edge effects and center of
glass conductance values with respect to different types of glazings
and
their sizes.

~Neeraj

Neeraj Kapoor
t: +91-99581.70018
Kalpakrit Sustainable Environments Pvt. Ltd.
New Delhi


Chris Jones wrote:
> A client has a project with the glazing units butt jointed at the
> vertical joints between sections.  He thinks that this may have less
> thermal bridging then for a vertical joint with typical framing
> details.  Does any one have any experience with this type of joint? 
> The glazing units are double pane sealed units with warm edge
spacers.
>
>
>
> Chris Jones, P.Eng.
> 14 Oneida Avenue
> Toronto, ON M5J2E3
> Tel. 416 203-7465
> Fax. 416 946-1005
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


      Best Jokes, Best Friends, Best Food and more. Go to http://in.promos.yahoo.com/groups/bestofyahoo/

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG




More information about the Bldg-sim mailing list