Assuming this is a fixed-speed centrifugal chiller, a reasonable first cut
is that the power is proportional to the lift (compressor pressure out-
pressure in).  Look at the refrigerant pressures at the expected condensing
and evaporating temperatures, and ratio the lift at the new condensing temp
to the lift at the old condensing temp.
 
This approach neglects the change in compressor efficiency that probably
occurs, but I've done this in the past prior to getting a complete chiller
map, and the approach works out pretty well.  It also matches with the
common rule of thumb that the power changes 1 to 2% per deg F change in
condensing temp.
 
With nagging, it may be possible to get a complete chiller map from the
manufacturer.  You can almost certainly get it in a competitive procurement
situation.
 
William E. Koran, P.E.
Senior Engineer
Q u E S T
Quantum Energy Services and Technologies
www.quest-world.com
 
  _____  

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Wyman, Kevin L
UTPWR
Sent: Tuesday, March 11, 2008 9:41 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Chiller Loads



I am trying to determine chiller power draw at reduced condensing
temperatures. The load is constant (100%) for all condensing temps. I have
manufacturer data for 100% 90% 80% ... 20% at both constant condensing
temperature (85F) and with ARI relief (but a partial loads).

Any suggestions to get full load kW/ton at different condensing
temperatures?

Thanks.



Kevin L. Wyman, P.E.
LEED AP
On-Site Power Product Management
UTC Power
195 Governor's Highway
South Windsor, CT 06074
(860) 727-7020 (V)
(860) 660-0723 (F)
(860) 882-9595 (M)
Kevin.wyman at utcpower.com 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080311/ede8be9a/attachment.htm 


More information about the Bldg-sim mailing list