in answer to the 1st question, add : 

BRINE-LOOP       = "Brine loop"

to the rink zone.  The "Brine loop" is the CHW loop the chiller is on -- 
this should add the rink load to your chiller.  Hope this helps.




tim wrote:
> A few Questions:
>  
> 1. I am modeling an ice arena with one ice rink in the main zone. I 
> know that the ice skating keywords available to DOE-2 cannot be 
> utilized through eQuest, but I included them in the input file anyhow 
> to effectively model the ice rink "behind the scenes". This has worked 
> thus far: the SIM report includes an annual load report for the ice 
> rink (RS-I) and the CHW loop reflects this load. However, the attached 
> chiller does not appear to see this load and thus does not use any 
> energy to meet it.
>  
> Has anyone tried this before and have any advice? I will assume that 
> raw DOE-2 would work and that trying this behind eQuest is the 
> problem, but I just want to try anyhow.
>  
> 2. Does anyone know of a source for Chiller performance curves for a 
> chiller capable of handling ice rink conditions? The loop temp is ~ 21 
> F and I have not ben able to locate any performace curve data for this 
> type of chiller yet.
>  
> 3. I have tried to extract the DOE-2 zip file from the website to my 
> C:\ but I get prompts demanding passwords (password protected files) 
> for all of the included files. I have looked at the Installation and 
> Execution instructions and I think I'm following them correctly, so am 
> I missing something?
>  
> Thanks,
> Tim
> ------------------------------------------------------------------------
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>   
> ------------------------------------------------------------------------
>
> No virus found in this incoming message.
> Checked by AVG Free Edition. 
> Version: 7.5.516 / Virus Database: 269.21.2/1305 - Release Date: 2/29/2008 6:32 PM
>   



More information about the Bldg-sim mailing list