[Bldg-sim] A question about ASHRAE baseline loop pump power

yizhao1 at vt.edu yizhao1 at vt.edu
Tue Jun 17 22:09:58 PDT 2008



Thanks! This works well. For setting up the pumps for water side systems that
serves more than 150,000 sf, my understanding is:
1. a loop (secondary) pump with VSD and a one speed(primary) pump for each
chiller;
2. a one speed conderser water loop pump, and one pump for each chiller,
which is the same pump in (1)
3. one VSD pump for each boiler, and no loop (secondary) pump

Is that correct?

Thanks in advance!

Ying
>
>
>
> Quoting Fred Porter <FPorter at archenergy.com>:
>
> > I deal with this by adjusting the "pipe-head" of the loop until the
> > total specific design pump power = 19 W/gpm, while still letting
> > eQuest/DOE2 "autosize" the pumps.
> >
> > I believe this W/gpm should be calculated as  (sum of all pump power
> > for both "primary" and "secondary" pumps connected to a loop)/design
> > loop flow. In addition to the loop (secondary) pump, the ASHRAE baseline
> > includes primary pumps, in DOE-speak, a "CHW-PUMP" and "CW-PUMP" for
> > each chiller, which is not the way eQuest sets things up by default. And
> > only the "primary" pump on the CW loop.
> > Fred
> >
> > >>> <yizhao1 at vt.edu> 6/17/2008 12:10 AM >>>
> >
> > Hi all –
> > I’m working on an ASHRAE baseline model with system #7 in eQuest.
> > ASHRAE
> > requires the chilled water loop pump power of 19W/gpm. So I ran the
> > model with
> > the default head and pump kW (left then blank) first, and found the gpm
> > of the
> > pump from the report, then I calculated and input the kW of the pump.
> > However,
> > after I ran the model again with this pump power, the pump gpm result
> > was
> > changed in the report. Also, I got a warning that said the pump flow
> > input is
> > lower than the actual flow. There is no input for a pump flow. So I
> > don’t know
> > what happened inside eQuest.
> >
> > Do you know what is wrong here? How to model the ASHRAE loop pump
> > power
> > correctly in eQuest?
> >
> > Thanks a lot!
> >
> >
> > Ying
> >