[Bldg-sim] A question about ASHRAE baseline loop pump power
Fred Porter
FPorter at archenergy.com
Tue Jun 17 05:35:30 PDT 2008
I deal with this by adjusting the "pipe-head" of the loop until the
total specific design pump power = 19 W/gpm, while still letting
eQuest/DOE2 "autosize" the pumps.
I believe this W/gpm should be calculated as (sum of all pump power
for both "primary" and "secondary" pumps connected to a loop)/design
loop flow. In addition to the loop (secondary) pump, the ASHRAE baseline
includes primary pumps, in DOE-speak, a "CHW-PUMP" and "CW-PUMP" for
each chiller, which is not the way eQuest sets things up by default. And
only the "primary" pump on the CW loop.
Fred
>>> <yizhao1 at vt.edu> 6/17/2008 12:10 AM >>>
Hi all –
I’m working on an ASHRAE baseline model with system #7 in eQuest.
ASHRAE
requires the chilled water loop pump power of 19W/gpm. So I ran the
model with
the default head and pump kW (left then blank) first, and found the gpm
of the
pump from the report, then I calculated and input the kW of the pump.
However,
after I ran the model again with this pump power, the pump gpm result
was
changed in the report. Also, I got a warning that said the pump flow
input is
lower than the actual flow. There is no input for a pump flow. So I
don’t know
what happened inside eQuest.
Do you know what is wrong here? How to model the ASHRAE loop pump
power
correctly in eQuest?
Thanks a lot!
Ying
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080617/edffc388/attachment.htm>
More information about the Bldg-sim
mailing list