James -

 

On the Window Library Detailed View screen in WINDOW 5, the Type field
controls the height and width of the window. There are several choices in
the pulldown list, which you can use if these fit your window - you will see
the dimensions change as you pick the different types. The last 3 options in
that Type pulldown list are "Custom" options - Custom Dual Vision
Horizontal, Custom Dual Vision Vertical, and Custom Single Vision. Selecting
one of these three choices will allow you to then input values in the Width
and Height input fields.

 

Robin Mitchell

Windows & Daylighting Group

Lawrence Berkeley National Laboratory

  _____  

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James Hess
Sent: Wednesday, June 11, 2008 3:54 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Window 5 program question

 

This question does not deal directly with a simulation program, but affects
a program that is used to calculate inputs that would go into a simulation
program such as eQuest.

 

I'm trying to use the Window5 program to correctly calculate overall window
properties (u-value, SHGC, VT, etc.) for a project.

 

Within the program I can't seem to be able to create a new window that has a
different width and height than the preprogrammed default --> 47.244" W by
59.055" H

 

The width and height are always grayed out and therefore unable to be
changed.

 

Does anybody know how to input different width and height values than the
default values?

 

Thanks a bunch for your help with this! :-)

 

Regards,

 

JAH 

 

James A.  Hess, PE, CEM

Energy Engineering Team Leader

TME, Inc.

5800 Evergreen Drive

Little Rock, AR  72205

 

ph   501-666-6776

fax  501-663-8888

cell  501-351-4667

jhess at tmecorp.com <mailto:email at tmecorp.com> 

www.tmecorp.com <http://www.tmecorp.com/> 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080611/f06f8253/attachment.htm>


More information about the Bldg-sim mailing list