[Bldg-sim] ASHRAE 90.1-App G: Site Shading
gail
gail22 at gmail.com
Wed Jun 4 14:00:37 PDT 2008
Appendix G does specifically state that for existing buildings being gutted,
the Baseline building envelope should be modeled based on the existing
conditions prior to any revisions that are part of the scope of work being
evaluated (Table G3.1(5)(f)). Therefore, if you are modeling self-shading
and adjacent buildings in the proposed case for an existing building, they
should also be modeled in the base case for existing buildings.
Best Regards,
Gail Stranske
CTG Energetics, Inc.
On Wed, Jun 4, 2008 at 1:32 PM, Demba Ndiaye <demba.ndiaye at setty.com> wrote:
> Eric,
>
>
>
> My understanding is that, regardless of the fact that the building is new
> or existing, there is no specific requirement regarding the modeling of
> neighboring shading objects.
>
>
>
> ______________
>
> Demba Ndiaye
> ------------------------------
>
> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Eric Studer
> *Sent:* Wednesday, June 04, 2008 3:47 PM
> *To:* bldg-sim at lists.onebuilding.org
> *Subject:* [Bldg-sim] ASHRAE 90.1-App G: Site Shading
>
>
>
> Hello,
>
>
>
> ASHRAE 90.1-2004 Appendix G has a clause pertaining to self-shading of the
> baseline building, but there does not seem to be any explicit direction
> regarding shading from other objects beyond the building envelope (trees,
> buildings, etc). Should the base case be modeled as being impacted by
> adjacent buildings or other objects? Would this be different for a new
> building versus an existing building that is being gutted?
>
>
>
> Thanks
>
>
>
> * *
>
>
>
> Eric Studer, PE, LEED AP
> DMI
> 35 Walnut Street
> Wellesley, MA 02481
> Ph: (781) 431-1100 ext 12
> Fax: (781) 431-1109
> e-mail: estuder at dmiinc.com
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080604/b8ebbec5/attachment.htm>
More information about the Bldg-sim
mailing list