[Bldg-sim] eQuest to Energy Pro: VRF

Eric Shadd EShadd at archenergy.com
Tue Jul 8 11:45:27 PDT 2008


I looked into doing this a month ago or so.  I didn't find a way for EnergyPro to read in BDL files.
 
My experience is that EnergyPro is really easy to use, as long as you keep track of your surface areas and spaces.  That's simply because there's no 3D representation, so if you make a mistake with record-keeping, you won't see it right away.  It's got copy/cut/paste for entire zones, and is built for Title 24 compliance (faster, more reliable, and better libraries than eQuest for this app). 
 
But for overall capabilities, it is missing a share of the capabilities that eQuest offers, so in my case, I had to create an EnergyPro model for Title 24, and eQuest model for parametric analysis.  Just as an example, I think in one case I couldn't put a VFD on a hot water pump.
 
-Eric

>>> <bldg-sim-request at lists.onebuilding.org> 7/7/2008 12:53 PM >>>
Send Bldg-sim mailing list submissions to
bldg-sim at lists.onebuilding.org 

To subscribe or unsubscribe via the World Wide Web, visit
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org 
or, via email, send a message with subject or body 'help' to
bldg-sim-request at lists.onebuilding.org 

You can reach the person managing the list at
bldg-sim-owner at lists.onebuilding.org 

When replying, please edit your Subject line so it is more specific
than "Re: Contents of Bldg-sim digest..."


Today's Topics:

   1. Energy Cost for Miscelleneous Equpiment Load (eric wang)
   2. eQUEST Weather Data File (Routh Consulting Engineers)
   3. Re: eQUEST Weather Data File (Aulbach, John)
   4. Sources for Actual Weather Data (Jeff Buscher)
   5. Re: Sources for Actual Weather Data (Howe, Timothy)
   6. Sources for Actual Weather Data - Clarification (David S Eldridge)
   7. eQuest to Energy Pro: VRF (Matthew Higgins)
   8. DesignBuilder Workshop at SimBuild 2008 (Mahabir Bhandari)
   9. Custom window layout duplication (Daniel Wilkerson)
  10. Shell vs. Floor Multipliers (Daniel Wilkerson)


----------------------------------------------------------------------

Message: 1
Date: Sun, 6 Jul 2008 21:58:58 -0700 (PDT)
From: eric wang <shaojieworld2006 at yahoo.com>
Subject: [Bldg-sim] Energy Cost for Miscelleneous Equpiment Load
To: bldg-sim at lists.onebuilding.org 
Message-ID: <749236.31991.qm at web58104.mail.re3.yahoo.com>
Content-Type: text/plain; charset="iso-8859-1"

Hello,
?
I defined the miscelleneous equipment load as internal load in my eQUEST baseline model. I can find the energy consumption in kwh in the detail output file. However, where could I find the energy cost for the miscelleneous equipment load because I want to make sure it is at least 25% of the total energy cost in the baseline model? I really appreciate if anyone can give me some hints.
?
Thank
?
Shaojie


      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080706/04980cc7/attachment.html>

------------------------------

Message: 2
Date: Mon, 7 Jul 2008 08:31:16 -0700
From: "Routh Consulting Engineers"
<routhconsultingengineers at charter.net>
Subject: [Bldg-sim] eQUEST Weather Data File
To: <bldg-sim at lists.onebuilding.org>
Message-ID: <2FDBCDADE8CA4B97A9177178E16F69C4 at D5T81241>
Content-Type: text/plain; charset="iso-8859-1"

Are the .BIN weather data files used by eQUEST in the same format as the .BIN packed weather data file that were used by DOE2.1E? I have some actual annual weather data files for my site that I use to run my models against actual utility data for the same year to help calibrate them. My clients are requesting current work to performed using eQUEST rather than DOE2.1E, but I wanted to be able to do these same calibration checks. If they are not in the same format, is there a conversion utility available?

Thanks in advance for anyone's reply,
Rick Routh
Routh Consulting Engineers, Inc.
P.O. Box 3187
Pasco, WA  99302
509-547-8262
509-542-0650 FAX
routhconsultingengineers at charter.net 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080707/400a4200/attachment-0001.htm>

------------------------------

Message: 3
Date: Mon, 7 Jul 2008 08:42:23 -0700
From: "Aulbach, John" <jaulbach at nexant.com>
Subject: Re: [Bldg-sim] eQUEST Weather Data File
To: "Routh Consulting Engineers"
<routhconsultingengineers at charter.net>,
<bldg-sim at lists.onebuilding.org>
Message-ID:
<99A2815FF4D295488E034407278B16A401F917A1 at sacexm01.nexant.corp>
Content-Type: text/plain; charset="us-ascii"

Same format. Should be no problem to run.

________________________________

From: bldg-sim-bounces at lists.onebuilding.org 
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Routh
Consulting Engineers
Sent: Monday, July 07, 2008 8:31 AM
To: bldg-sim at lists.onebuilding.org 
Subject: [Bldg-sim] eQUEST Weather Data File


Are the .BIN weather data files used by eQUEST in the same format as the
.BIN packed weather data file that were used by DOE2.1E? I have some
actual annual weather data files for my site that I use to run my models
against actual utility data for the same year to help calibrate them. My
clients are requesting current work to performed using eQUEST rather
than DOE2.1E, but I wanted to be able to do these same calibration
checks. If they are not in the same format, is there a conversion
utility available?

Thanks in advance for anyone's reply,
Rick Routh
Routh Consulting Engineers, Inc.
P.O. Box 3187
Pasco, WA  99302
509-547-8262
509-542-0650 FAX
routhconsultingengineers at charter.net 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080707/7dee80d2/attachment-0001.htm>

------------------------------

Message: 4
Date: Mon, 07 Jul 2008 12:12:36 -0400
From: Jeff Buscher <jeff.buscher at gmail.com>
Subject: [Bldg-sim] Sources for Actual Weather Data
To: bldg-sim at lists.onebuilding.org 
Message-ID: <48724074.6020908 at gmail.com>
Content-Type: text/plain; charset=ISO-8859-1; format=flowed

I'm modeling an existing building in Trane Trace and have utility data 
for the last two years.  I'd like to replace the TMY2 weather data in my 
model with actual hourly data.   Can anyone point me to information on 
where to obtain real hourly data in TMY2 format?

Jeff Buscher, PE
Essential Systems Engineering
109 Central Ave
Asheville, NC  28801


------------------------------

Message: 5
Date: Mon, 7 Jul 2008 10:27:32 -0600
From: "Howe, Timothy" <Timothy.Howe at stantec.com>
Subject: Re: [Bldg-sim] Sources for Actual Weather Data
To: "Jeff Buscher" <jeff.buscher at gmail.com>,
<bldg-sim at lists.onebuilding.org>
Message-ID:
<21B0B92BAE9B75458CA9781211D5330302169B60 at CD1001-M200.corp.ads>
Content-Type: text/plain;charset="us-ascii"

http://rredc.nrel.gov/solar/old_data/nsrdb/1991-2005/tmy3/ 


Timothy Howe, MS, LEED(r) AP
Mechanical Engineer
Stantec

The content of this email is the confidential property of Stantec and
should not be copied, modified, retransmitted, or used for any purpose
except with Stantec's written authorization. If you are not the intended
recipient, please delete all copies and notify us immediately.

Please consider the environment before printing this email.

-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org 
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jeff
Buscher
Sent: Monday, July 07, 2008 12:13 PM
To: bldg-sim at lists.onebuilding.org 
Subject: [Bldg-sim] Sources for Actual Weather Data

I'm modeling an existing building in Trane Trace and have utility data
for the last two years.  I'd like to replace the TMY2 weather data in my

model with actual hourly data.   Can anyone point me to information on 
where to obtain real hourly data in TMY2 format?

Jeff Buscher, PE
Essential Systems Engineering
109 Central Ave
Asheville, NC  28801
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org 
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG 



------------------------------

Message: 6
Date: Mon, 7 Jul 2008 12:38:40 -0500
From: David S Eldridge <DSE at grummanbutkus.com>
Subject: [Bldg-sim] Sources for Actual Weather Data - Clarification
To: "bldg-sim at lists.onebuilding.org" <bldg-sim at lists.onebuilding.org>
Message-ID:
<44C8483B27AECE40BD175796F571A16684E3FC67 at IL-COM.il.grummanbutkus.com>
Content-Type: text/plain; charset="us-ascii"

Just in case there was some confusion, the TMY3 (like TMY2) are not continuous periods of chronological time, they are 12 individual months often from different years that are combined to form one "average" or typical year for simulation purposes.

So the data are (mostly) actual hourly weather observations, but not for one continuous year that would correspond with the utility bills.

David


> -----Original Message-----
>
> http://rredc.nrel.gov/solar/old_data/nsrdb/1991-2005/tmy3/ 
>
>
>
> -----Original Message-----
>
> I'm modeling an existing building in Trane Trace and have utility data
> for the last two years.  I'd like to replace the TMY2 weather data in my
>
> model with actual hourly data.   Can anyone point me to information on
> where to obtain real hourly data in TMY2 format?
>



------------------------------

Message: 7
Date: Mon, 07 Jul 2008 12:11:49 -0600
From: Matthew Higgins <higgins at edi-arch.com>
Subject: [Bldg-sim] eQuest to Energy Pro: VRF
To: bldg-sim at lists.onebuilding.org 
Message-ID: <48725C65.6010102 at edi-arch.com>
Content-Type: text/plain; charset=us-ascii; format=flowed

Does any one know whether or not eQuest BDL can be trascribed into 
Energy Pro software? I ask because I don't want to duplicate the efforts 
already exerted in eQuest to be able to model a VRF system in Energy Pro.

On that same note, is Energy Pro all that different than eQuest? (In 
terms of the capabilities/inputs/interface/learning-curve/etc.)

-- 
Matthew Higgins, LEED AP
Technical Specialist
Environmental Dynamics, Inc.
Architecture and Sustainability Consulting Services
505.242.2851

Any data provided by the Consultant, verbal or written, are to be considered opinions of building energy and/or daylight performance. The Client understands that the Consultant has no control of occupant habits, equipment or material performance or characteristics, site or climate conditions or the Contractor's method of assembly, and that the Consultant's opinions regarding building energy/daylight performance are made on the basis of the Consultant's professional judgment and experience. The Consultant makes no warranty, express or implied, that the energy/daylight performance of the building will not vary from the Consultant's opinion of building energy/daylight performance.




------------------------------

Message: 8
Date: Mon, 7 Jul 2008 14:08:46 -0400
From: "Mahabir Bhandari" <Bhandari at DesignBuildersoftware.com>
Subject: [Bldg-sim] DesignBuilder Workshop at SimBuild 2008
To: <bldg-sim at lists.onebuilding.org>
Message-ID: <013701c8e05c$813e83b0$83bb8b10$@com>
Content-Type: text/plain; charset="us-ascii"


Introduction to DesignBuilder Software - One day workshop  


August 02, 2008, Saturday  - (Immediately After SimBuild 2008 conference)
University of California, Berkeley

The objective of this workshop is to introduce DesignBuilder to the users
and simulators who would like to use EnergyPlus simulation tool to model
energy performance of buildings, but without the complexities of working
with arcane input file editor. DesignBuilder is the most comprehensive and
powerful graphical user interface for EnergyPlus. This hands-on training
will provide general overview and introduction to building energy analysis
using DesignBuilder. The trainees will learn to quickly setup a building
model, change the building parameters using components and templates and run
the simulation



For more information and registration, please visit: 



http://www.designbuildersoftware.com/db_workshop.php 



Early registration deadline is July, 15.



Mahabir

____________________________________________________________________________
___

Mahabir Bhandari, Ph.D.
DesignBuilder Software| 18 Tanglewood Rd | Amherst, MA 01002 | Ph: (413)
256-4647 | www.designbuildersoftware.com 
____________________________________________________________________________
___



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080707/8ebb7b44/attachment-0001.htm>

------------------------------

Message: 9
Date: Mon, 7 Jul 2008 14:46:36 -0400
From: Daniel Wilkerson <DWilkerson at DWYER.COM>
Subject: [Bldg-sim] Custom window layout duplication
To: "bldg-sim at lists.onebuilding.org" <bldg-sim at lists.onebuilding.org>
Message-ID:
<2938629EE8D9074AB7407B5DD55667923275A22811 at EMAIL.DWYER.COM>
Content-Type: text/plain; charset="us-ascii"

Hey All,

I (painstakingly) entered a custom window layout in DD mode on a 4-floor multifamily mid-rise shell, but only the first floor in the shell displays my window layout whether I use the Floor Multiplier or not.  Does anyone know how I can duplicate my custom window layout for all of the floors in the shell? I assumed it would do this with the floor multiplier.  Thanks!

     -Dan

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080707/c893283c/attachment-0001.htm>

------------------------------

Message: 10
Date: Mon, 7 Jul 2008 15:26:35 -0400
From: Daniel Wilkerson <DWilkerson at DWYER.COM>
Subject: [Bldg-sim] Shell vs. Floor Multipliers
To: "equest-users at lists.onebuilding.org"
<equest-users at lists.onebuilding.org>,
"bldg-sim at lists.onebuilding.org" <bldg-sim at lists.onebuilding.org>
Message-ID:
<2938629EE8D9074AB7407B5DD55667923275A2281D at EMAIL.DWYER.COM>
Content-Type: text/plain; charset="us-ascii"

Hey All,

Are Shell Multipliers and Floor Multipliers the same thing? If not, what is the difference?  Thanks a lot!

     -Dan
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080707/6ee4c6bd/attachment-0001.htm>

------------------------------

_______________________________________________
Bldg-sim mailing list
Bldg-sim at lists.onebuilding.org 
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org 


End of Bldg-sim Digest, Vol 8, Issue 6
**************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080708/22ef4794/attachment-0001.htm>


More information about the Bldg-sim mailing list