[Bldg-sim] Appendix G: Cooled space?
Kevin Kyte
kkyte at robsonwoese.com
Tue Jul 1 08:40:53 PDT 2008
Did anyone come up with an answer for this? I have a similar situation. My
thought would be that it should be considered a cooling system.
Kevin Kyte, EIT, LEED AP
RobsonWoese, Inc.
(T) 716-636-1800
(F) 716-636-1856
<http://robsonwoese.com/index.php> http://robsonwoese.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Chatfield, Gary
Sent: Monday, June 30, 2008 12:04 PM
To: Howe, Timothy; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G: Cooled space?
Tim
My thoughts on this would be that your main system should be sized to
provide the fresh air at your cooling temperature to replace the air
rejected by the exhaust, and you will probably find this is happening unless
your space is negatively pressurized.
Gary Chatfield
LEEDR AP
FLACK + KURTZ
385 Pilot Road, Suite D. Las Vegas, NV 89119
Main: 702.897.8181
Direct: 702.352.9562
Fax: 702.914.6966
<mailto:gary.chatfield at lv.fk.com> gary.chatfield at lv.fk.com
_____
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Howe, Timothy
Sent: Thursday, June 26, 2008 6:47 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G: Cooled space?
I have a mechanical room that is conditioned to 95 in cooling through
exhaust fans and heated to 65 with unit heaters.
Do the exhaust fans constitute as a cooling system? The system would need
to provide a sensible capacity of 5 btu/h*ft2 for the mech room to be
considered to be a cooled space, which I have not yet calculated.
The reason I as is that if these exhaust fans are not considered a cooling
system then the baseline cooling system will need to be modeled to complete
an accurate LEED model.
Any suggestions?
Tim.
Timothy Howe, MS, LEEDR AP
Mechanical Engineer
Stantec
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080701/a1477bc0/attachment-0001.htm>
More information about the Bldg-sim
mailing list