[Bldg-sim] 90.1 VAV Baseline Min CFM/SF = 0.4 or Ventilation

Paul Riemer Paul.Riemer at dunhameng.com
Thu Jul 31 13:30:40 PDT 2008


Mike,
Addendum AM revised G3.1.3.13 to alternatively allow the zone minimum ventilation flow, but I get lost when I think about how that is supposed to be calculated.

Is the minimum ventilation air the same as the % OA at the system or is it the zone minimum OA without any multi-space impacts?
Remembering that Std 62's method for determining system level OA in a multi-space VAV system is dependent on
1) the zone design flow rate which you are now auto sizing
2) the zone minimum zone flow rate which you are trying to determine

G3.1.25 is clear that minimum ventilation rates should be the same between the models (excepting DCV) and that kind of makes sense at a system level.  But potential collisions still exist when system supply air volume is lower than the minimum outside air volume or when you want to claim ventilation effectiveness impacts.

Whatever you come up, with eQUEST will accept a minimum cfm/sf in the detailed mode.
Paul Riemer

-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Demba Ndiaye
Sent: Thursday, July 31, 2008 2:49 PM
To: Tobias, Mike; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] 90.1 VAV Baseline

Mike,

Section G3.1.3.13 calls for a minimum of 0.4 cfm/ft2 of floor area
served. Use this number as your minimum flow.

______________
Demba Ndiaye
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-
> bounces at lists.onebuilding.org] On Behalf Of Tobias, Mike
> Sent: Thursday, July 31, 2008 3:42 PM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] 90.1 VAV Baseline
>
> My baseline system is System 5: Packaged VAV w/ reheat, but 90.1
doesn't
> specify the minimum airflow percentage and I'm not sure what to use.
> Equest defaults the min VAV airflow at 40% in core zones and 30% in
> perimeter zones.  Increasing this number to 100% (cv) nearly doubles
the
> heating energy.  Since this is such a sensitive number, it's accuracy
is
> critical, what do you think I should use?
>
> -Mike
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-
> UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG


More information about the Bldg-sim mailing list