[Bldg-sim] LEED EA Cr1 and historing building alteration

Bishop, Bill bbishop at PathfinderEngineers.com
Fri Feb 29 09:07:13 PST 2008


Ramana,

 

I posted this two days ago:

 

"What if it is an existing building, in which case, "the baseline
building design shall reflect existing conditions prior to any revisions
that are part of the scope of work being evaluated."  (From Table G3.1
No. 5 (f).)  Do I ignore items (a) through (e) in their entirety,
including no self-shading (and, for that matter, the whole
average-of-four-orientations requirement)?  And there is still the
question of shading from adjacent buildings."

 

So your LEED baseline should reflect the existing building envelope,
including fenestration.  (But I am still uncertain about ignoring items
(a) through (e) in Table G3.1 No.5.)

 

Also note that in the LEED NC 2.2 Errata posted 10/31/2007, the text for
the entire Credit EAc1 has been replaced.  (I have not done a
line-by-line comparison to see what changed.):

 

https://www.usgbc.org/ShowFile.aspx?DocumentID=3198  

 

Regards,

 

William Bishop, EIT, LEED(r) AP | Pathfinder Engineers LLP

Mechanical Engineer


3300 Monroe Ave., Suite 306 
Rochester, NY  14618

TEL (585) 218-0730 Ext. 114
FAX (585) 218-0737 

bbishop at pathfinderengineers.com

 

www.pathfinderengineers.com

P Please consider the environment before printing this email

________________________________

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ramana Koti
Sent: Friday, February 29, 2008 11:45 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] LEED EA Cr1 and historing building alteration

 

Dear all,

How does changing the glazing of a historic building affect the way it's
modeled in the baseline case for LEED EA Cr1? Would the baseline have to
be ASHRAE 90.1 compliant or can it still be an exception?

Thanks,

Ramana Koti, LEED AP
Sustainable Building Analyst

ELEMENTS division of BNIM architects
106 W. 14th Street Suite 200
Kansas City, Missouri 64105

p 816.783.1635 f 816.783.1501
www.bnim.com| elements.bnim.com 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080229/8ff42090/attachment.htm>


More information about the Bldg-sim mailing list