[Bldg-sim] error message: LOOP has zero flow- ABORTING-- Pleasehelp!

Brandon Nichols BrandonN at Hargis.biz
Thu Feb 21 04:21:42 PST 2008


Hi Linda,
 
Check to be certain that there  exists terminal equipment in your
project containing hydronic heating coils which are actually attached to
the loop in question -- Hot Water Loop B.   An easy way to check this is
to look at the 'Waterside HVAC' tree --  I'll bet you don't see any
systems under the loop in question.
 
Perhaps are all attached to Hot Water Loop A, or the ones you think that
are attached to Loop B have furnaces instead of hydronic heating coils.
 
The error you're getting essentially indicates zero demand for heating
hot water on the loop.
 
HTH...
 
Brandon Nichols, PE, LEED(r) AP 
Mechanical
HARGIS ENGINEERS 
600 Stewart Street 
Suite 1000 
Seattle, WA 98101 
www.hargis.biz <http://www.hargis.biz/>  

d | 206.436.0400 c | 206.228.8707
o | 206.448.3376  f | 206.448.4450 

 

  _____  

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Lam, Linda
Sent: Wednesday, February 20, 2008 6:22 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] error message: LOOP has zero flow- ABORTING--
Pleasehelp!



To All:

 

Thanks to everyone who has helped me with previous questions.  I am
fairly new at energy simulation and I have learned a lot so far from
just getting emails off this listserve-

 

I am getting an eQUest error message: LOOP has zero flow- ABORTING.  And
a message after wards:

"Errors during HVAC simulation setup or design calculations. See .sim
file for details. Terminating Run."

I cannot find this .sim file...

 

I have eQuest autosizing my boilers, chillers and pump GPM's.  In the
detailed data output report, the error message says:

***ERROR****************************************************************
*******

             Loop: Hot Water Loop B                 has zero design
flow.

             Check input for consistency, or specify design loads.

 

If anyone's had this experience or has a solution, I'd really appreciate
your help!

 

Thanks!

 

Linda Lam

  FLACK + KURTZ

405 Howard St.

Suite 500

San Francisco, CA 94105

http://www.flackandkurtz.com <http://www.flackandkurtz.com/>   

415.398.3833 Main

415.402.5813 Direct

415.433.5311 Fax
linda.lam at sf.fk.com

Ensuring that today's built environment preserves the natural
environment in which we live.

This e-mail may contain confidential and/or privileged information. If
you are not the intended recipient (or have received this e-mail in
error) please notify the sender immediately and destroy this e-mail.
Any unauthorized copying, disclosure or distribution of the material in
this email is strictly forbidden.

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080221/e4920076/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 837 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080221/e4920076/attachment.gif>


More information about the Bldg-sim mailing list