[Bldg-sim] Metal Building R-19 cavity insulation U-factor
JRR
Energy.wwind at cox.net
Wed Feb 13 08:58:58 PST 2008
Jrr wrote;
Steel studs without Styrofoam sheathing is a loosing design choice. Period.
The XPS sheathing should be 1" or 1.5" ; 3/4 inch is not enough.
Energy 10 will calculate the effective R values in a handy format. So
will TREAT.
Kevin Kyte wrote:
>This may help.
>
>
>
>http://www.maconline.org/designalert.PDF
>
>
>
>
>
>
>
>Kevin Kyte, LEED AP
>
>RobsonWoese, Inc.
>
>(T) 716-636-1800
>
>(F) 716-636-1856
>
> <http://robsonwoese.com/index.php> http://robsonwoese.com
>
>
>
>From: bldg-sim-bounces at lists.onebuilding.org
>[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Howe, Timothy
>Sent: Tuesday, February 12, 2008 1:07 PM
>To: bldg-sim at lists.onebuilding.org
>Subject: [Bldg-sim] Metal Building R-19 cavity insulation U-factor
>
>
>
>I have a metal building wall construction with R-19 insulation between the
>girts.
>
>
>
>Now in ASHRAE 90.1-2004 Appendix A, Table A3.2 the single layer of mineral
>fiber only goes up to R-13.
>
>
>
>Any suggestion on how to determine the U-Factor for this wall?
>
>
>
>Thanks.
>
>
>
>Tim.
>
>
>
>
>
>
>
>Timothy Howe
>Mechanical Engineer
>Stantec
>
>
>
>
>------------------------------------------------------------------------
>
>_______________________________________________
>Bldg-sim mailing list
>Bldg-sim at lists.onebuilding.org
>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>
>