[Bldg-sim] eQuest Default f(PLR) Skepticism
Robby Oylear
robbyo at rushingco.com
Mon Feb 4 11:28:32 PST 2008
Okay, I think I understand now. The EIR fPLR curve is not actually a
correction to the EIR efficiency, but to the total power draw of the
chiller. I was calculating EIRFPLR as EIR(current conditions)/ EIR
(design conditions), when eQUEST wants it in the format of a power draw at
current conditions divided by the power draw at design conditions.
This also clears up another question I had which was why eQUEST calculates
the total power draw as a function of full load operating capacity and not
the actual load. The EIRFPLR curve corrects it.
After fixing my equation the EIRFPLR values I received from the
manufacturer are within 2-7% of eQUEST default curves.
Thanks all for your help!
Robby Oylear
Project Engineer
direct: 206.788.4571
cell: 206.354.2721
www.rushingco.com
-----Original Message-----
From: John Aulbach [mailto:jra_sac at yahoo.com]
Sent: Monday, February 04, 2008 10:35 AM
To: Robby Oylear; 'Aulbach, John'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] eQuest Default f(PLR) Skepticism
I am sure we would welcome typical chiller data that
minimally complys.Remember that IPLV allows condenser
water relief for their calculations. eQuest needs
three curves including the kW/ton at CONSTANT
condenser water - then the program will "jump a curve"
to move the kW/ton to its location based on outdoor
air AND point on the part load curve.
Not always consistant, part load vs. outdoor air. I
believe Steve Gates has a comment on that in the
BLDG-SIM archives.
__________________________________________________________________________
__________
Be a better friend, newshound, and
know-it-all with Yahoo! Mobile. Try it now.
http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080204/e979e0c8/attachment.htm>
More information about the Bldg-sim
mailing list