[Bldg-sim] FW:
Keohane, Michael
Michael.Keohane at pmg.ie
Tue Dec 2 08:27:50 PST 2008
I am currently building a Baseline Model for system 8 with PFP in IESVE
for compliance with ASHRAE 90.1 2004 Appendix G. I am not familiar with
the VAV PFP or ASHRAE 90.1 and this is my first attempt to model it. I
am modeling an office building which has significant glazed facades in
climate zone 4a.
1. Can anybody tell me does the design air flow rate temperature
difference of 20 F apply for heating as well as cooling? (G3.1.2.8
2. If it applies for heating also what happens when the parallel fan
is sized at 50% of the peak design airflow and is insufficient to
provide heating to the space at the temperature difference of 15C, can
the parallel fan airflow rate be increased from 50% to take account for
the additional heating requirement? (G3.1.3.14)
3. If the heating loads are larger (and therefore the airflow rates)
then the cooling loads then, do I still size the parallel fan at 50% of
the cooling load or do I size based on 50% of the heating load, or do I
increase this fan volume and the electrical reheat to provide the
required capacity for the larger heating loads? Or is the primary
airflow increased at elevated temperatures to make up the difference.
I am confused so any help on this would be appreciated
Regards
Michael Keohane
An example of sizing Fan Terminal Units (FTU)....
I have a 1000 cfm zone (determined from peak load conditions) to be
served by a FTU, therefore the parallel fan in my box is sized for 500
cfm (50% of peak flow). Now typically in heating is when the primary
air is going to go to an absolute minimum. This must be 300 cfm or the
total volume of OSA that I need for the zone, whichever is larger. In
theory, the fan could provide all 500 cfm of its air when the primary
air is at a minimum if that meets the load. The fan will typically
always be the first stage of heating. After that, if setpoint isn't
met, the reheat coil comes on. I would say that the design condition,
depending on climate of course, will be cooling dominated 7 times out of
10.
Also, as a note, the discussion of minimum flow setpoint is an area of
weakness for a VAV system. If the zone was designed for 1000 cfm in
cooling mode and the minimum outside air was determined to be 300 cfm,
you will almost never reach this value when the VAV is operating at part
load. There is a good article on this in the January issue of
Engineered Systems magazine.
Hope this helps.
Regards,
Andrew Craig, EIT,LEED AP/ Mechanical Designer
INTERFACE ENGINEERING
direct 503.382.2696
________________________________
From: Chien Si Harriman [mailto:chien.harriman at iesve.com
<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org> ]
Sent: Thursday, February 21, 2008 2:25 PM
To: Andrew Craig
Cc: bldg-sim at lists.onebuilding.org
<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>
Subject: FW: [Bldg-sim] FW:
Hi Andrew, that is really helpful. I missed that section of the code.
Now, a few points that maybe someone could elucidate, maybe even you:
1.) Does 50% of the peak design flow rate imply that, if, for example,
the min vol setpoint is 30%, then the recirc coming in parallel is 20%?
2.) That makes sense, except I am guessing this CFM value is the 50%
peak design flow rate? That would only be logical.
3.) This min setpoint is for the primary air.
4.) The design condition they are referring to is the summer design
condition, or the winter design condition or both? I am guessing it is
both.
That is a great help, thanks for everything so far.
Sincerely,
Chien
________________________________
From: Andrew Craig [mailto:andrew_c at ieice.com
<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org> ]
Sent: Thu 21/02/2008 22:12
To: Chien Si Harriman; bldg-sim at lists.onebuilding.org
<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>
Subject: RE: [Bldg-sim] FW:
Chien---
Section G3.1.3.14 of Appendix G hit on requirements for fan powered
boxes. They are:
1.) FTUs shall be sized for 50% of the peak design flow rate
2.) FTUs shall be modeled with 0.35 W/cfm fan power.
3.) Minimum volume setpoints for FTUs shall be equal to 30% of the
peak design flow rate or the rate required to meet minimum OSA
ventilation, whichever is larger.
4.) The supply air temperature setpoint shall be constant at the
design condition.
Hope that helps. Good luck.
Regards,
Andrew Craig, EIT,LEED AP/ Mechanical Designer
INTERFACE ENGINEERING
direct 503.382.2696
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>
[mailto:bldg-sim-bounces at lists.onebuilding.org
<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org> ]
On Behalf Of Chien Si
Harriman
Sent: Thursday, February 21, 2008 2:07 PM
To: bldg-sim at lists.onebuilding.org
<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>
Subject: [Bldg-sim] FW:
________________________________
From: Chien Si Harriman
Sent: Thu 21/02/2008 21:46
To: bldg-sim at lists.onebuilding.org
<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>
Subject:
Hi there-
I've been tasked with modeling a parallel fan powered box as my baseline
system for ASHRAE 90.1 Appendix G, and basically I am wondering if there
is anyone who knows of modeling guidelines for that FPB? I have the
capability of modeling any sort of conditions I would like, so I can
vary the flow rate of the recirc air, the control sequencing of the
fan-assist, and even whether that fan is variable volume or constant
volume.
I can't find any guidelines that exist anywhere on this topic in ASHRAE
90.1, and this is the first time I've had to model it (I've never
designed an electrically-heated building before). Does anyone know
whether:
1.) There is a specific ratio for the amount of recirc air to minimum
primary air?
2.) Whether the amount of recirc air should vary (ie-a variable speed
fan)?
3.) You can just use a real FPB with data from a company like Carrier,
and just call it a day on the simultion effort?
Any guidance would be really helpful.
Thanks in advance,
Chien Harriman
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachme
nts/20080221/ac273dea/attachment.html
<http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachm
ents/20080221/ac273dea/attachment.html>
________________________________
size=2 width="100%" align=center>
* Previous message: [Bldg-sim] FW: FW:
<http://lists.onebuilding.org/htdig.cgi/bldg-sim-onebuilding.org/2008-Fe
bruary/006971.html>
* Next message: [Bldg-sim] FW:
<http://lists.onebuilding.org/htdig.cgi/bldg-sim-onebuilding.org/2008-Fe
bruary/006974.html>
* Messages sorted by: [ date ]
<http://lists.onebuilding.org/htdig.cgi/bldg-sim-onebuilding.org/2008-Fe
bruary/date.html#6973> [ thread ]
<http://lists.onebuilding.org/htdig.cgi/bldg-sim-onebuilding.org/2008-Fe
bruary/thread.html#6973> [ subject ]
<http://lists.onebuilding.org/htdig.cgi/bldg-sim-onebuilding.org/2008-Fe
bruary/subject.html#6973> [ author ]
<http://lists.onebuilding.org/htdig.cgi/bldg-sim-onebuilding.org/2008-Fe
bruary/author.html#6973>
________________________________
More information about the Bldg-sim mailing list
<http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org>
*********************************************************************************************
'50 Best Companies to work for 2007 and 2008' Great Place to Work Institute
*********************************************************************************************
'Outstanding Achievement Award' Irish Institute of Training and Development
*********************************************************************************************
2008 Best Workplaces in Europe
*********************************************************************************************
Project Management Limited is a private company limited by shares, registered in Ireland. Registered Number: 048273. Registered Office: Killakee House, Belgard Square, Tallaght, Dublin 24, Ireland. Project Management Limited is an indirect subsidiary of Project Management Holdings Limited t/a PM Group a private company limited by shares, registered in Ireland. Registered Number: 122309. Registered Office: Killakee House, Belgard Square, Tallaght, Dublin 24, Ireland. The PM Group contains a number of subsidiary companies, full details of which are published on our website http://www.pmg.ie.
The information contained in this electronic message (e-mail), and any files transmitted with it, is intended for the named recipient(s) only. It may contain privileged and/or confidential information and if you are not the intended recipient, you must not copy, distribute or take any action in reliance on it. If you have received this electronic message (e-mail), and any files transmitted with it, in error, please delete it immediately.
Internet communications are not secure and therefore PM Group does not accept legal responsibility for the contents of this message. Except where sent in the ordinary course of business, any views or opinions presented are solely those of the author and do not necessarily represent those of the PM Group.
PM Group operates anti-virus programs; nevertheless all attachments with this message should be checked for viruses before it is opened. PM Group cannot be held responsible for failure by the recipient to test for viruses before opening any attachments and does not accept responsibility for any damage whatsoever that is caused by viruses being passed.
Should you communicate with anyone at PM Group by e-mail you consent to us monitoring and reading any such correspondence. Email is monitored by PM Group solely for operational, security and business reasons.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081202/276e9fd6/attachment-0001.htm>
More information about the Bldg-sim
mailing list