Dear Ulrik,
 
Since the intent of the Standard is to assign the better glazing performance
to non-North walls, I always rotate the glazing characteristics with the
building. (e.g., I assign the "North" glazing characteristics to the
elevation that, after rotating, faces North)
 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

 

  _____  

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ulrik
Welle-Strand Horn
Sent: Monday, December 01, 2008 7:30 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G - Base Case Orientations and Glazing


Dear all,

When you are rotating the building through 4 different orientations, do you
change the glazing so that the glazing with the highest SHGC is always faces
north, or do you put the glazing with high SHGC on the original north
facade, and then rotate the building so that the high SHGC glazing faces the
east, south and west orientations in subsequent simulations?

Yours faithfully,


Ulrik Welle-Strand Horn 
Sustainability Engineer


Silpa Inc.
s i m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e

AMERICAS | MIDDLE EAST | ASIA
www.silpainc.com <http://www.silpainc.com/> 


India: +91.90080.96083

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081201/5760c682/attachment.htm>


More information about the Bldg-sim mailing list