[Bldg-sim] Variable Speed Screw Chiller Curves
Demba Ndiaye
demba.ndiaye at setty.com
Tue Aug 26 12:30:38 PDT 2008
Can you please share with us the source of these curves?
______________
Demba Ndiaye
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Dan Nall
Sent: Tuesday, August 26, 2008 3:17 PM
To: Kingsley,Michael L.; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Variable Speed Screw Chiller Curves
Try these on for size;
"VFDSCrew EIR fPLR" = CURVE-FIT
TYPE = CUBIC
INPUT-TYPE = DATA
INDEPENDENT = ( 1, 0.75, 0.5, 0.25 )
DEPENDENT = ( 1, 0.97307, 1.01436, 1.3616 )
..
"Carrier-EIR-fCHWT&CWT" = CURVE-FIT
TYPE = BI-QUADRATIC-T
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( 0.767051, -0.0236208, 0.0004375, 0.0024939, 0.0002337,
-0.000418 )
..
"Carrier-EIR-fPLR&dT" = CURVE-FIT
TYPE = BI-QUADRATIC-RATIO&DT
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( -0.0230025, 0.902964, 0.0935993, 0.00347819,
-2.45759e-005, -0.00196462 )
..
"Carrier-CAP-fCHWT&CWT" = CURVE-FIT
TYPE = BI-QUADRATIC-T
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( 0.448509, 0.0185587, -0.00028125, 0.00306901,
-5.0201e-005, 0.000108475 )
-----Original Message-----
From: "Kingsley, Michael L."
Sent: Aug 26, 2008 2:15 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Variable Speed Screw Chiller Curves
Does anyone have DOE-2 performance curves for a variable speed screw chiller (I believe the Carrier Evergreen 23XRV is the only one now) that they would be willing to share?
Thanks in advance.