[Bldg-sim] multiple wall constructions for LEED

Brian Tysoe BTysoe at mcw.com
Mon Aug 11 14:40:40 PDT 2008


Chien,

Have a look at Table G3.1 in ASHRAE 90.1-2004. As far as I can tell, above-grade walls in the baseline case are to be modeled as steel-framed using the assembly maximum U-factor from Tables 5.5.

Regards,


Brian Tysoe M.Sc., LEED AP

MCW Consultants Ltd. <http://www.mcw.com>
600-156 Front Street West
Toronto, ON M5J 2L6
Phone 416-598-2920
Fax 416-598-5394

This e-mail may be privileged and confidential. Any unauthorized use is strictly prohibited. If you received this e-mail in error, please contact the sender directly.

________________________________
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Chien Si Harriman
Sent: August 11, 2008 5:21 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] multiple wall constructions for LEED

Hi all-

A quick, but kind of hazy question for me at least, regarding LEED projects.  Let's just say, that a building is composed of multiple wall types, spanning a range of the ASHRAE 90.1 definitions...some portions of the building is steel framed, another portion is mass wall, and yet another portion is wood framed, for example.  In this case, what would the baseline be defined as?  Does each wall remain categorically intact, and you simply choose the baseline U-factor that corresponds to that wall type, or do you have to determine the wall type that makes up the majority of the proposed building, and choose this wall type as the baseline wall type?

Thanks in advance,
Chien