I've been getting some warnings in a model I'm currently working on, and
I haven't been able to find a way to fix them.
 
The warnings are as follows:
 
 
**WARNING***************************************************************
*******
             PREHEAT/HEATING-CAPACITY in SYSTEM M AHU-26 (VAV)

             is too low to provide the requested supply temperature for
             the calculated mixed air temperature using total ZONE loads
             (on LS-A/B) and SYSTEM design parameters, plus outside air
             conditions (on LS-C), and specified capacities & air flows.
             Requested temperature is  55.00 calculated is  10.37
             Check HEATING-CAPACITY, HEAT-SET-T, PRE-HEAT-T,
MAX-SUPPLY-T,
             DESIGN-HEAT-T, and ZONE loads for consistency.
 
 
AHU-26 is a PIU system (series boxes).  Zone outside airflow is set up
at 20 CFM / person, the # of people is accurate, and the system is set
up to size the minimum OA based on the sum of the zone OA.
 
I can't figure out what's going on....it almost seems like the system is
not returning any air, and is at 100% OA.  But my OA is set to a fixed
fraction, and inputing an arbitrary supply CFM doesn't change the mixed
air temp warning at all (still 10.37).
 
I know it's hard to diagnose a problem without being able to open the
file (I'm happy to send someone the .inp and .pd2 files), but has anyone
run into this problem before?
 
Thanks!
 

GHT Limited
James Hansen, PE, LEED AP

Senior Associate

1010 N. Glebe Rd, Suite 200

Arlington, VA  22201-4749

703-338-5754 (Direct)

703-243-1200 (Office)

703-276-1376 (Fax)

www.ghtltd.com <http://www.ghtltd.com/> 

 

The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to ght at ghtltd.com, and destroy this communication and all copies thereof, including all attachments.  Thank you.



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080806/ab7bb6e3/attachment-0001.htm>


More information about the Bldg-sim mailing list