[Bldg-sim] Process Loads in Warehouse

Zhai Chaoqin crithy at gmail.com
Fri Aug 1 06:20:14 PDT 2008


I found two references for the process and plug load in warehouses:
1) a PNNL report entitled Development of Advanced Energy Design Guide for
Small Warehouse and Storage Buildings. The value given is 0.35 W/sf.
2) a NREL report entitled Energy Savings Modeling and Inspection Guidelines
for Commercial Building Federal Tax Deductions. The value given is 0.43
W/sf.

So it looks to me ~0.4W/sf is a reasonable number.

Chaoqin Zhai

On Tue, Jul 29, 2008 at 9:18 PM, Duke Graham <duke at gaiadevelopment.com>wrote:

>  I think this is a quick question.
>
> Does anyone know the typical value for process/receptacle loads (W/sf) in
> warehouse areas, probably given in AHRAE 90.1 User's Manual?
>
> Any help would be appreciated.
>
> Thanks,
>
>
>
>
>
>
>
> [image: Gaia New 4-29-08]
>
>
>
> Duke Graham, LEED*(R) *AP
>
> *Gaia Development LLC*
>
> 4040 Del Rey Ave., Suite 12
>
> Marina del Rey, CA 90292
>
> p. 310.591.8172
>
> f.  310.827.1702
>
> www.gaiadevelopment.com<http://../../Local%20Settings/Temporary%20Internet%20Files/Content.Outlook/WUXQZ3ZP/www.gaiadevelopment.com>
>
>
>
> P Please consider the trees before printing this email
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080801/a071ab3a/attachment-0001.htm>


More information about the Bldg-sim mailing list