Hi Bungane,
Yes, in Appendix G a high-rise residential building w/ heating source of
fossil fuel, fossil/electric hybrid, & purchased heat, the baseline system
is a PTAC. If the heat source is electric or other, the baseline system is
a PTHP.
Amanda Bogner, PE LEED AP
404.806.2018 EXT 103
404.806.2019 FAX
_____
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Bungane
Mehlomakulu
Sent: Wednesday, August 27, 2008 11:38 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] LEED ASHRAE 90.1-2004 Appendix G Standard Bldg
Can someone please confirm that according the ASHRAE 90.1-2004 Appendix G
the baseline HVAC System for High-Rise Residential is a PTAC unit?!
I've reviewed definitions in ASHRASE 90.1-2004 and building codes and
everything points to ASHRAE 90.1-2004 classifying the baseline HVAC System
for Residential (inclusive of high-rise) as a PTAC Unit under Appendix G. I
realize the Energy Cost Budget method has a different baseline system.
Thanks,
Bungane Mehlomakulu, PE
Senior Associate, LEED AP
IBE Consulting Engineers
14130 Riverside Drive Suite 201
Sherman Oaks, CA 91423
p: (818) 377-8220 ext. 237
f: (818) 377-8230
<http://www.ibece.com> IDEAS FOR THE BUILT ENVIRONMENT
This e-mail message, including any attachments, is for the sole use of the
intended recipient(s) and may contain confidential and privileged
information. Any unauthorized review, use, disclosure, or distribution is
prohibited. If you are not the intended recipient, please contact the sender
by reply e-mail and destroy all copies of the original message.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080827/04ee2d03/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/bmp
Size: 24894 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080827/04ee2d03/attachment.bin>
More information about the Bldg-sim
mailing list