[Bldg-sim] Variable Speed Screw Chiller Curves

Steven Gates stvgates at pacbell.net
Tue Aug 26 14:05:04 PDT 2008


They are based on published data from one of the major chiller
manufacturers.  While specific to that manufacturer, they are believed to be
representative of that class of chillers.

  _____  

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Demba Ndiaye
Sent: Tuesday, August 26, 2008 12:31 PM
To: Dan Nall; Kingsley,Michael L.; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Variable Speed Screw Chiller Curves

 

Can you please share with us the source of these curves?

 

______________

Demba Ndiaye

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Dan Nall
Sent: Tuesday, August 26, 2008 3:17 PM
To: Kingsley,Michael L.; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Variable Speed Screw Chiller Curves

 

Try these on for size;

"VFDSCrew EIR fPLR" = CURVE-FIT 

TYPE = CUBIC

INPUT-TYPE = DATA

INDEPENDENT = ( 1, 0.75, 0.5, 0.25 )

DEPENDENT = ( 1, 0.97307, 1.01436, 1.3616 )

..

"Carrier-EIR-fCHWT&CWT" = CURVE-FIT 

TYPE = BI-QUADRATIC-T

INPUT-TYPE = COEFFICIENTS

COEFFICIENTS = ( 0.767051, -0.0236208, 0.0004375, 0.0024939, 0.0002337, 

-0.000418 )

..

"Carrier-EIR-fPLR&dT" = CURVE-FIT 

TYPE = BI-QUADRATIC-RATIO&DT

INPUT-TYPE = COEFFICIENTS

COEFFICIENTS = ( -0.0230025, 0.902964, 0.0935993, 0.00347819, 

-2.45759e-005, -0.00196462 )

..

"Carrier-CAP-fCHWT&CWT" = CURVE-FIT 

TYPE = BI-QUADRATIC-T

INPUT-TYPE = COEFFICIENTS

COEFFICIENTS = ( 0.448509, 0.0185587, -0.00028125, 0.00306901, 

-5.0201e-005, 0.000108475 )




 

-----Original Message----- 
From: "Kingsley, Michael L." 
Sent: Aug 26, 2008 2:15 PM 
To: bldg-sim at lists.onebuilding.org 
Subject: [Bldg-sim] Variable Speed Screw Chiller Curves 



Does anyone have DOE-2 performance curves for a variable speed screw chiller
(I believe the Carrier Evergreen 23XRV is the only one now) that they would
be willing to share?

 

Thanks in advance.

 

Michael Kingsley

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080826/7ac9dde0/attachment.htm>


More information about the Bldg-sim mailing list