[Bldg-sim] Baseboard heaters in VAV system
Andrew Craig
AndrewC at InterfaceEng.Com
Thu Aug 21 08:40:30 PDT 2008
James---
In my opinion, baseboards act a little funny in eQUEST. This is how
I've made the scenario you describe work:
Under the Heating tab of your unit (Coil Cap/Control), restore the
default in the reheat entry so it is blank. Make sure the Hot Water
Loop is still enabled as the zone heating source though. Under the
Preheat/Baseboard tab, specify Baseboard Source as the Hot Water Loop.
You can change the default entries for the baseboards (pressure drop,
delta T, valve, etc.) if applicable. Then for each perimeter zone, go
into the heating tab and change the Baseboard control to Thermostatic if
it isn't already selected. I've had trouble getting the Outdoor Reset
selection to work and most of our projects have baseboards controlled by
thermostats anyway. You can also enter the capacity of the baseboards
for each zone or let the system self-size. This should work...if not
I'd be happy to look at the inp.
Regards,
Andrew Craig, EIT,LEED AP/ Mechanical Designer
INTERFACE ENGINEERING
direct 503.382.2696
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James
Hansen
Sent: Thursday, August 21, 2008 8:18 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Baseboard heaters in VAV system
I've got a building that cools with shutoff VAV boxes and heats with
perimeter hydronic baseboard heaters.
When I'm setting up my system, do I specify hot water baseboard heaters
and leave the Zone Heat Source set to "Not Installed", or do I specify a
hot water loop for the Zone Heat Source, and eQuest knows to apply this
to the baseboard heaters and NOT the shutoff VAV boxes?
I currently have the Zone Heat Source as "Not Installed", but it appears
from my SS-R reports that there are hundreds of hours of underheating,
so something is not working correctly. I've had my hot water loop set
to snap, demand, and scheduled, so I think the loop is running
correctly.
Thanks in advance!
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Direct)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
________________________________
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee. It is
the property of GHT Limited. Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful. If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com
<mailto:ght at ghtltd.com> , and destroy this communication and all copies
thereof, including all attachments. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080821/66599b2a/attachment.htm>
More information about the Bldg-sim
mailing list