[Bldg-sim] PTAC and PTHP EER, fan energy

Michael Tillou michael.tillou at gmail.com
Fri Apr 18 13:15:45 PDT 2008


The issue is slightly more complicated for unitary equipment over 5 tons
because the ARI 340/360 testing standard for determining the EER of larger
unitary equipment has pre-defined limits on the allowed fan ESP during test
conditions.  If you are simulating packaged equipment that is designed with
higher external fan static pressures than required by ARI 340/360 and you
use the as-designed fan power or fan power allowed by ASHRAE90.1 for
calculating "Cooling-Only" EER,  you will over-estimate cooling energy
savings.  This issues applies to Appendix G baseline systems 3,4,5 and 7 and
any as-designed equipment whose performance is covered by ARI 340/360 (see
minimum efficiency tables in Chapter 6 of ASHRAE 90).  
 
For packaged equipment over 5 tons you should estimate fan power at the ARI
340/360 test conditions when separating EER into fan and cooling energy
components rather than using rated fan power or the ASHRAE fan power
allowance.
 
 
Mike
 
Michael Tillou, PE, LEED
P: 413-458-9870 C: 413-652-1087


  _____  

From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Loren Appin
Sent: Friday, April 18, 2008 2:30 AM
To: Michael Rosenberg
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] PTAC and PTHP EER, fan energy


Could anyone else comment on this?  I had asked this question a couple of
months ago, and through some research and guidance received the answer that:

The EER does include the fan power, which you would calculate from Table
6.8.1.D and you would calculate this for each system based upon it's
auto-sized capacity; thus, you will use a different EER for each system.

An important clause to then look at is G3.1.2.1 which states that equipment
efficiencies must be broken down into their component parts, such as the EER
into EIR and fan power.  One way of doing this is to parse it out using
equest, capturing the correct EIR and then plugging that back in with a
separate fan power.

To get the fan power you would use Table G3.1.2.9 to get BHP and calculate
the fan power from this.

All of this, though, is according to ASHRAE 2004, I have not been using the
2007 Addendum.  I just wanted to see if this is what everyone else has been
doing?

Thanks

Loren Appin

Energy Engineer

Silpa Inc.
s i m p l e  .  s c i e n t i f i c  .  s u s t a i n a b l e
AMERICAS | ASIA
www.silpainc.com <http://www.silpainc.com/> 




On Thu, Apr 17, 2008 at 7:26 PM, Michael Rosenberg
<Michael.Rosenberg at state.or.us> wrote:


The EER does include the fan power. The baseline fan power allowance in
Appendix G from 90.1 2004 was recognized as being much too high for PTACs
and PTHPs. An addendum was issued lowering the value to 0.3 W/cfm. This is
captured in the new 2007 version of 90.1 Appendix G.

Michael Rosenberg
Oregon Department of Energy
625 Marion St. N.E.
Salem, OR 97301-3742
Phone : (503) 373-7809
Fax: (503) 373-7806

>>> "Xu, Xiaowei" <xiaowei.xu at ny.fk.com> 4/17/2008 8:10:25 AM >>>

Hi,

I have a quick question about the EER requirement for the PTAC and PTHP
system. In Standard 2004, Table 6.8.1D gives out the minimum requirement
for the PTAC and PTHP system. My question is does this EER include the
fan power or not?



Also for the PTAC and PTHP system, following the Appendix G fan power
energy calculation, the fan power would be about 0.7~0.8W/cfm. However
the manufacture's catalog data usually gives out the value around
0.2~0.3W/cfm, which means the proposed case would get a lot of fan
energy savings. Does this make sense? Thanks a lot.





Xiaowei Xu

Engineer

 FLACK + KURTZ

475 Fifth Avenue

New York, NY 10017




http://www.flackandkurtz.com <http://www.flackandkurtz.com/>


212.532.9600 Main

212.951.2662 Direct

212.689.7489 Fax
xiaowei.xu at ny.fk.com

Ensuring that today's built environment preserves the natural
environment in which we live.

This e-mail may contain confidential and/or privileged information. If
you are not the intended recipient (or have received this e-mail in
error) please notify the sender immediately and destroy this e-mail.
Any unauthorized copying, disclosure or distribution of the material in
this email is strictly forbidden.





_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG





-- 
Loren Appin | loren.appin at gmail.com 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080418/38f3dbf4/attachment.htm 


More information about the Bldg-sim mailing list