[Bldg-sim] PTAC and PTHP EER, fan energy

Xu, Xiaowei xiaowei.xu at ny.fk.com
Thu Apr 17 08:10:25 PDT 2008


Hi,

I have a quick question about the EER requirement for the PTAC and PTHP
system. In Standard 2004, Table 6.8.1D gives out the minimum requirement
for the PTAC and PTHP system. My question is does this EER include the
fan power or not?

 

Also for the PTAC and PTHP system, following the Appendix G fan power
energy calculation, the fan power would be about 0.7~0.8W/cfm. However
the manufacture's catalog data usually gives out the value around
0.2~0.3W/cfm, which means the proposed case would get a lot of fan
energy savings. Does this make sense? Thanks a lot.

 

 

Xiaowei Xu

Engineer          

  FLACK + KURTZ

475 Fifth Avenue

New York, NY 10017

 

http://www.flackandkurtz.com <http://www.flackandkurtz.com/>   

212.532.9600 Main

212.951.2662 Direct

212.689.7489 Fax
xiaowei.xu at ny.fk.com

Ensuring that today's built environment preserves the natural
environment in which we live.

This e-mail may contain confidential and/or privileged information. If
you are not the intended recipient (or have received this e-mail in
error) please notify the sender immediately and destroy this e-mail.
Any unauthorized copying, disclosure or distribution of the material in
this email is strictly forbidden.

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080417/cbe06810/attachment.htm 
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 837 bytes
Desc: image001.gif
Url : http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080417/cbe06810/attachment.gif 


More information about the Bldg-sim mailing list