[BLDG-SIM] Exterior Lighting
Karen Walkerman
kwalkerman at gmail.com
Wed Sep 12 06:30:57 PDT 2007
Hi Mark,
In detailed interface, go to "Utility and Economics" and open your Electric
energy meter (EM1). Under "Direct Loads" you should see a number that
corresponds to the exterior lighting value you entered in the wizard. There
will also be a schedule associated with it. This was created from the
"dayshape" entered in the wizard and can be modified, though not as
elegantly as in the wizard.
~Karen~
On 9/11/07, Zoeteman, Mark R. <mrzoeteman at ftch.com> wrote:
>
> In eQUEST:
>
> How do you change exterior lighting watts in detailed interface that were
> entered in wizard?
> How do you change exterior lighting dayshape in detailed interface that
> gets created from wizard input?
>
> Mark Zoeteman, FTC&H